I'm not sure how the wording got revised over the years, but back-in-the day 
the standard was a lot clearer that the residual pressure was measured at the 
base of the riser. Here is what the old note used to say under the table for 
Water Supply Requirements for Pipe Schedule Sprinkler Systems:

        NOTES:
        1. The pressure required at the base of the sprinkler riser(s) shall be 
the residual pressure required under the roof plus the  pressure required to 
reach this elevation.

Whenever I've done such evaluations, the analysis would take into account the 
losses due to elevation and friction losses in the underground piping, between 
the water supply at the street and the base of the riser, based on flowing the 
Acceptable Flow at Base of Riser (Including Hose Stream Allowance) from the 
table.

Then I would factor in the loss through the backflow preventer and the pressure 
due to the elevation to the highest sprinkler. Thus determining the residual 
pressure under the roof.

Since the evaluation is for existing systems, the Minimum Residual Pressure 
Required only needs to be the 15 psi for light hazard  or the 20 psi for 
ordinary hazard.  The 50 psi value is only for new systems thar are greater 
than 5000 sq.ft.  For the new system, I would usually opt to calculate  it 
hydraulically.

It should be recognized that the above is my personal opinion and not that as a 
member of the NFPA and should therefore not be considered, nor relied upon, as 
the official position of the the NFPA, nor any of their technical committees.

Best regards,

Larry Keeping. P.Eng.
Senior Technical Specialist

PLC FIRE SAFETY SOLUTIONS
3413 Wolfedale Road, Suite 7
Mississauga, ON L5C 1V8

Phone:       905-949-2755 Ext 204
Fax:            905-949-1752
Email:         [email protected]
Website:    www.plcfire.com
Toll Free:   1-800-675-2755



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Jamie Seidl via Sprinklerforum
Sent: June 4, 2021 4:14 PM
To: Sprinklerforum <[email protected]>
Cc: Jamie Seidl <[email protected]>
Subject: pipe schedule/residual pressure

Warning! This email came from outside your company.

I am looking at a project where we are renovating an existing building with a 
new system.  There are other buildings on the site (1930's vintage) that share 
the underground lines.  To bring the site into compliance with current codes, 
RPZ backflows are being added at the entrance to the site.
The existing buildings are occupied, and the fire department is looking for 
some assurance that the systems will work with the addition of the backflow 
preventer.  I remembered (though have never applied it) section 11.2.2.8 allows 
for the calculation of the residual pressure at the highest sprinkler, and 
deducting elevation, BFP losses ect...  The buildings in question are over 5000 
sqft, so the minimum 50 psi will apply.
So my question is, do I just utilize the residual pressure from the closest 
hydrant, deduct the elevation and backflow losses from the residual and call it 
a day?  Or do I need to account for additional friction through the system 
piping?  Both 13 and the handbook seem to be mute on this.
Thanks again, Forumites.
Jamie  Seidl
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to