Yeah, that pretty much describes the proposed setup.  Two primary pumps at 1500 
each to meet a 2900 gpm demand. Third pump in the house is for redundancy.

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 
[email protected] | www.jacobs.com
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: email or MS TEAMS

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Travis Mack via Sprinklerforum
Sent: Monday, June 21, 2021 10:54 AM
To: [email protected]
Cc: [email protected]
Subject: [EXTERNAL] RE: Calculating Parallel fire pumps

We've done this where there is a need for redundant pumps.  Let's assume you 
need a 3000 gpm pump.  A second 3000 gpm pump is quite expensive.  The 
contractors had us set it up as (2) 1500 gpm pumps for a 3000 gpm total 
capacity.  Then, you need a redundant pump in case one is down, so then you 
just have a 1500 gpm backup in case one goes down.  AutoSprink was able to 
calculate that.

We have also done some jobs with demands in the 10,000+ gpm range.  You need 
parallel pumps to make that work.  AutoSprink could calculate that without 
issue.  You just have to draw it up properly.

Travis Mack, CFPS, CWBSP, RME-G, COC, SET Engineering Manager MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271 ext. 700 C: 480-272-2471
[email protected]<mailto:[email protected]>
https://urldefense.com/v3/__http://www.mfpdesign.com__;!!B5cixuoO7ltTeg!TbhbVfeVYScuQbgWTaK5_QrjN4ennB3fPRXxf9fzmS-8Y1xry_7_iBOEHayufOfuRA$
 
<https://urldefense.com/v3/__http://www.mfpdesign.com__;!!B5cixuoO7ltTeg!TbhbVfeVYScuQbgWTaK5_QrjN4ennB3fPRXxf9fzmS-8Y1xry_7_iBOEHayufOfuRA$
 >

Send large files to us via: 
https://urldefense.com/v3/__https://www.hightail.com/u/MFPDesign__;!!B5cixuoO7ltTeg!TbhbVfeVYScuQbgWTaK5_QrjN4ennB3fPRXxf9fzmS-8Y1xry_7_iBOEHax4mtJYQA$
 
<https://urldefense.com/v3/__https://na01.safelinks.protection.outlook.com/?url=https*3A*2F*2Fwww.hightail.com*2Fu*2FMFPDesign&data=02*7C01*7C*7C1121d49f9e6b4cf248f108d4df580e77*7C14e5497c16da42e69ffa77d19bafe511*7C0*7C0*7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5*2BAZvlHhABSexWY*3D&reserved=0__;JSUlJSUlJSUlJSUlJSU!!B5cixuoO7ltTeg!TbhbVfeVYScuQbgWTaK5_QrjN4ennB3fPRXxf9fzmS-8Y1xry_7_iBOEHazg27rPDQ$
 >

From: Sprinklerforum <[email protected]> On Behalf 
Of Prahl, Craig/GVL via Sprinklerforum
Sent: Monday, June 21, 2021 7:50 AM
To: [email protected]
Cc: Prahl, Craig/GVL <[email protected]>; Matt Grise <[email protected]>
Subject: RE: Calculating Parallel fire pumps

What's the logic? Who knows. I know how this should be done and this isn't 
going to accomplish anything except just to complicate the design. The issue 
is, one building we have exceeds the 150% out of a single pump so with what 
they want to use, one pump won't make it unless we actually select it properly.

I'm still trying to work through this mess and see if we cannot persuade them 
to not follow this concept.

No, the "expert" is not a pump vendor, just a desk jockey with a 
self-proclaimed brilliant idea.

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 
[email protected]<mailto:[email protected]> | 
http://www.jacobs.com<http://www.jacobs.com>
1041 East Butler Road Greenville, South Carolina 29606 CONTACT BY: email or MS 
TEAMS

-----Original Message-----
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Matt Grise via Sprinklerforum
Sent: Monday, June 21, 2021 10:44 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Matt Grise <[email protected]<mailto:[email protected]>>
Subject: [EXTERNAL] RE: Calculating Parallel fire pumps

What is the goal of having 2 pumps? If you want full redundancy, could you just 
calculate the system one pump at a time? It seems like having them both running 
would be a better-case scenario that would result in added safety. Are they 
trying to get by with 2 smaller pumps?

I think AutoSprink might be able to do it. You would want to confirm with 
AutoSprink (MEP CAD), but I am pretty sure that we have calculated multiple 
source systems with it before.

I don't suppose your quantum expert is also a pump vendor?

Matt


-----Original Message-----
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Prahl, Craig/GVL via Sprinklerforum
Sent: Monday, June 21, 2021 9:37 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Prahl, Craig/GVL <[email protected]<mailto:[email protected]>>
Subject: Calculating Parallel fire pumps

We have a project in one of the Arab states. We are following a little bit of 
the UFC and some of the local codes.

The owner wants two pumps selected at 50% of the required capacity instead of 
one pump as we would normally provide. His thought is that pump 1 comes on and 
runs at 50% of it's rating and then pump two comes on and runs at 50% to meet 
the total system demand. Yeah, I know, don't laugh.

And we've tried to talk them out of this arrangement since it will not work as 
they expect but someone who is thinks they are an expert in Quantum 
Inter-Planetary Fire Protection Hydro-Physics thinks this is a great idea.


We use HASS for hydraulic calcs and it does not have the ability calculate 
using two pumps in parallel.

Can AutoSprink or Hydracad calculate this kind of pump arrangement?


Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 
[email protected]<mailto:[email protected]> | 
http://www.jacobs.com<http://www.jacobs.com>
1041 East Butler Road Greenville, South Carolina 29606 CONTACT BY: email or MS 
TEAMS


________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http*3a*2f*2flists.firesprinkler.org*2flistinfo.cgi*2fsprinklerforum-firesprinkler.org&c=E,1,UOX-iwkiNtxi6q8KlNBiL45QsTVPBtn3ETYP3KvtGsQS2rjRYJH4hYDy99c9T7rVBUfYz4P5b9UsJ0IR03DG5JV81y4xVheLpkcis6az0WapiyoL49sETkyjgA,,&typo=1__;JSUlJSU!!B5cixuoO7ltTeg!VdgVsSAh6wA9TT3AcYEjow4cCv35tq5JzRPCtp69uwUyVuFVRl4S0y-HPAAsiaT6aQ$<https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http*3a*2f*2flists.firesprinkler.org*2flistinfo.cgi*2fsprinklerforum-firesprinkler.org&c=E,1,UOX-iwkiNtxi6q8KlNBiL45QsTVPBtn3ETYP3KvtGsQS2rjRYJH4hYDy99c9T7rVBUfYz4P5b9UsJ0IR03DG5JV81y4xVheLpkcis6az0WapiyoL49sETkyjgA,,&typo=1__;JSUlJSU!!B5cixuoO7ltTeg!VdgVsSAh6wA9TT3AcYEjow4cCv35tq5JzRPCtp69uwUyVuFVRl4S0y-HPAAsiaT6aQ$>
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!VdgVsSAh6wA9TT3AcYEjow4cCv35tq5JzRPCtp69uwUyVuFVRl4S0y-HPABrQPJLnA$<https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!VdgVsSAh6wA9TT3AcYEjow4cCv35tq5JzRPCtp69uwUyVuFVRl4S0y-HPABrQPJLnA$>

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!TbhbVfeVYScuQbgWTaK5_QrjN4ennB3fPRXxf9fzmS-8Y1xry_7_iBOEHaxysx7A2w$
 
<https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!TbhbVfeVYScuQbgWTaK5_QrjN4ennB3fPRXxf9fzmS-8Y1xry_7_iBOEHaxysx7A2w$
 > _______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!TbhbVfeVYScuQbgWTaK5_QrjN4ennB3fPRXxf9fzmS-8Y1xry_7_iBOEHaxysx7A2w$

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to