What is the opinion of the group, when you have 1" wide metal slats, 4" deep, & 
6" on center.
Sprinklers are installed above slats, in a ACT ceiling, 14" above the top of 
the slats.
Are these an obstruction?
According to NFPA 13 2019 (9.3.10) open grid ceiling, you need 18" minimum at a 
10'x10' spacing, and there is only 14"
Or can 10.2.7.2.1.3, 3x rule apply? 4" deep times 3 = 12"

Dennis Wilson
Blackhawk Sprinklers
1-319-266-7721