Language was added to NFPA 20 a few cycles ago - EH2 for a diesel driven
fire pump system.

NFPA 20 - 2019 edition

4.14.1.3 Fire Pump Building or Rooms with Diesel Engines. Fire pump
buildings or rooms enclosing diesel engine pump drivers and day tanks shall
be protected with an automatic sprinkler system installed in accordance
with NFPA 13 as an Extra Hazard Group 2 occupancy.


*The above is my opinion and has not been processed as a formal
interpretation in accordance with the NFPA Regulations Governing Committee
Projects. This is provided with the understanding that the AFSA assumes no
liability for this opinion or actions taken on it and they are not to be
considered the official position of the **AFSA, and/or NFPA or its
technical committees.**AFSA cannot provide design or consulting engineering
services, and this opinion should therefore not be considered, nor relied
upon, as such.*

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Our members are at the heart of everything we do.*


*Don’t miss another issue!*

Sign-up to get your exclusive copy of the industry’s leading membership
magazine *Sprinkler Age* <https://sprinklerage.com/subscribe/> delivered
straight to your mailbox, inbox, or both! Subscribe now to get the latest
information you need to know and never miss another issue.


On Mon, Sep 13, 2021 at 1:48 PM Prahl, Craig/GVL via Sprinklerforum <
[email protected]> wrote:

> If you look at the definitions in NFPA 13 of the various occupancies, the
> presence of diesel fuel (combustible liquid) would dictate an EH2.
>
> With electric pumps OH1 or OH2 would be fine.
>
> Craig Prahl | Jacobs | Group Lead/SME - Fire Protection |
> [email protected] | www.jacobs.com
> 1041 East Butler Road   Greenville, South Carolina  29606
> CONTACT BY: email or MS TEAMS
>
>
>
> -----Original Message-----
> From: Sprinklerforum <[email protected]> On
> Behalf Of James Crawford via Sprinklerforum
> Sent: Monday, September 13, 2021 1:43 PM
> To: [email protected]
> Cc: James Crawford <[email protected]>
> Subject: [EXTERNAL] Fire Pump Room Sprinkler Classification
>
> We are having a discussion in our and with a local AHJ on the design
> requirements of the sprinkler system in a fire pump room with a diesel fire
> pump.
>
> Comments have varied from OH2 to EX1 to EH2
>
> Any feed back out there?
>
> Thank You
>
> James Crawford
> Phaser Fire Protection Ltd.
> Phone 604-888-0318
> Cel: 604-790-0938
> Email [email protected]<mailto:[email protected]>
> Web:
> https://urldefense.com/v3/__http://www.phaserfire.ca__;!!B5cixuoO7ltTeg!VeW9MkqZMmcPED-a0wA7RwhAfQ9ekKbI-XGRCR5BXJpBngHfsWeWJWDi_Ck0p1mH6g$
> <
> https://urldefense.com/v3/__http://www.phaserfire.ca__;!!B5cixuoO7ltTeg!VeW9MkqZMmcPED-a0wA7RwhAfQ9ekKbI-XGRCR5BXJpBngHfsWeWJWDi_Ck0p1mH6g$
> >
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!VeW9MkqZMmcPED-a0wA7RwhAfQ9ekKbI-XGRCR5BXJpBngHfsWeWJWDi_CkUz7yIVA$
>
> ________________________________
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any
> viewing, copying or distribution of, or reliance on this message by
> unintended recipients is strictly prohibited. If you have received this
> message in error, please notify us immediately by replying to the message
> and deleting it from your computer.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to