I think you are correct for your described situation: you have a
noncombustible overhang, under 4 ft, with no storage underneath, then no
sprinklers is OK.

It sure seems to me like we don't have to install sprinklers under
*combustible* overhangs 4 ft or less as long as there is no storage
underneath. It doesn't say this explicitly (it just doesn't require
sprinklers there, it doesn't specifically omit them), so maybe there is a
reason for that?


-Skyler


On Tue, Oct 5, 2021, 6:40 PM James Crawford via Sprinklerforum <
[email protected]> wrote:

> We have been discussing exterior projections in the office and with an AHJ
> on when sprinklers are required.
>
> Section 8.15.7.1 Unless the requirements of 8.15.7.2, 8.15.7.3. or
> 8.15.7.3 are met, sprinklers shall be installed under exterior projections
> exceeding 4'-0" in width.
>
> Section 8.15.7.5 Sprinklers shall be installed under exterior projections
> greater than 2'-0" wide over areas where combustibles are stored.
>
> Canopy is less than 4'-0" in width, No vehicle storage, non-combustible
> construction, not a corridor, so all items are met for 8.15.7.1, no
> sprinklers required.
>
> But 8.15.7.5 seems to requires them because the canopy is over 2'-0"
>
> Normally we worked on the assumption less than 4'-0" and non-combustible,
> no storage, no sprinklers required and the 2'-0" was for combustible
> construction, over 2'-0" you required sprotection.
>
> What are we missing
>
> Thank You
>
> James Crawford
> Phaser Fire Protection Ltd.
> Phone 604-888-0318
> Cel: 604-790-0938
> Email [email protected]<mailto:[email protected]>
> Web: www.phaserfire.ca<http://www.phaserfire.ca>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
  • NFPA #13... James Crawford via Sprinklerforum
    • Re:... Skyler Bilbo via Sprinklerforum
      • ... Jones, William - Fire Plans Examiner/Inspector via Sprinklerforum
        • ... Ken Wagoner via Sprinklerforum
          • ... Jones, William - Fire Plans Examiner/Inspector via Sprinklerforum
    • RE:... Mike Morey via Sprinklerforum

Reply via email to