No building size is indicated. Does the building code require protection?  
Plastic storage may be considered a high hazard.
If protection is a code requirement then the attic requires protection.
Without protection a fire in the attic will likely cause a total loss of the
building and contents.

Art Tiroly

ATCO Fire Protection


-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of Mike Morey via Sprinklerforum
Sent: Wednesday, October 06, 2021 10:59 AM
To: [email protected]
Cc: Mike Morey <[email protected]>
Subject: Attic protection over a storage occupancy

Applicable code/standards would be IBC 2012 and its references (NFPA 13 2010
mainly) I'm not coming up with a "why not" for this, but it doesn't give me
a warm fuzzy.  I have a wood framed "pole barn" being used for plastic
storage in racks.  The building is a standard 4:12 wood truss building with
plywood sheathing at the bottom of the trusses (with a layer of fiberglass
batts on them above) creating a flat ceiling at 18' AFF, walls are exposed
2x construction with fiberglass batts.  I can't come up with a reason I
can't protect the space below the plywood according to the storage
requirements (looking at .6/2600 dry system, rack storage of Gp A plastic to
20' max <5' clear, doing CMDA both because they barely have 18" clear and
they want a dry system) and the space above as an unused light hazard attic,
potentially with "back to back" style attic heads.  Anyone see a flaw with
this logic, or any other pitfalls to watch for due to this construction
scenario?  I don't love this scenario but the customer went out of their way
to avoid sprinklering the building origina  lly and built it to the bottom
dollar, but now a new insurance carrier may require it to be protected.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 /  cell
260.417.0625 /  fax 260.487.7991 email [email protected]



This message is for the named person's use only.  It may contain
confidential, proprietary or legally privileged information. No
confidentiality or privilege is waived or lost by any mistransmission.  If
you receive this message in error, please  immediately delete it and all
copies of it from your system, destroy any hard copies of it and notify the
sender.  You must not, directly or indirectly, use, disclose, distribute,
print, or copy any part of this message if you are not the intended
recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to