If we are referring to the six flexible coupling seismic separation assembly 
that every contractor finds an alternative, make a sizable wager with the 
structural engineer that the assembly provides vertical movement. Make sure the 
winnings cover the cost of six ½” pvc fittings and a four foot stick of ½” pvc 
pipe. Make the thing up and fool with it for some time before you present your 
case so that you can move it around to show it off like you know what you are 
doing, because at first it might look awkward enough that the engineer will cry 
foul. By the way, the details for this six coupling assembly show vertical 
accommodation in the elevation detail.
 You might obfuscate the demonstration by asking how much differential seismic 
movement this engineer is really expecting. Differential seismic lateral motion 
is due to how easy it is for one structural building section to be different in 
lateral flexibility than the next building section, i.e. across the seismic 
separation joint. Each building section will wiggle differently than the next. 
The difference shows up at the joint. Vertical differential flexibility, in 
other words “pogoing” differently than the next structural section is not 
happening very much, if any. Buildings are relatively much more vertically 
stiff than they are horizontally stiff. I might bet the structural engineer has 
not tried to calculate this. What might be the case, like this building is in 
Houston Texas which I believe has more seismic faults going on than any other 
US city, is that the structural engineer knows the building project has to span 
a known fault and so the structure is actually anticipating differential 
vertical movement at the joint.
Allan Seidel
St. Louis, MO  

> On Oct 19, 2021, at 11:45 AM, Steve Leyton via Sprinklerforum 
> <[email protected]> wrote:
> 
> A question was raised by a project structural engineer about the NFPA 13 
> seismic joint detail shown in Fig. A.9.3.3(a), 2016 edition for reference.    
> Does anyone know if this configuration has ever been tested/measured?   Has 
> it been verified as an acceptable OMNI-DIRECTIONAL solution?    The engineer 
> in question is looking at the detail and in his judgement, it's only a 2D 
> solution.   There are lateral and longitudinal movements shown, but not a 
> vertical one.    If there are installation or hanger/bracing committee people 
> who can chime in, I'm wondering if this figure has been vetted and that's why 
> it's still in the standard.   Bottom line:  Is Fig. A.9.3.3(a) equivalent to 
> a listed seismic loop?
> 
> 
> Steve Leyton, President
> Protection Design and Consulting
> T  |  619.255.8964 x 102  |  
> www.protectiondesign.com<http://www.protectiondesign.com/>
> 2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108
> Fire Protection System Design | Consulting | Planning | Training
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to