Matt,
The UL 203 and FM testing did not find their way into the standard,
however the ACI pre-qualification criteria was included beginning with
the 2010 edition. My memory of those discussions from so long ago is
that this was added to -13 after some discussions and input from member
of the committee who were structural engineers.
ACI 355.2 covers the pre-qualifications of such post-installed anchors,
and ACI 318 deals with building code requirements for structural
concrete. An ICC-ESR document provides information on anchors
manufactured by various companies (Hilti, Powers, Simpson, etc) and the
capabilities of their products to meet the criteria established in 355.2.
Please note that there is no such requirement in -13 for pre-set anchors
in concrete, or for anchors used as a means to fasten the hanger to the
structure.
As I am a current principal member of the NFPA 13 hanging and bracing
committees, please see the disclaimer below.
sincerely,
*Ken Wagoner, SET*
*Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235*
*Phone: (760) 745-6181 *
*Visit the website
<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>
IMPORTANT NOTICE: This correspondence is not a Formal Interpretation
issued pursuant to NFPA Regulations. Any opinion expressed is the
personal opinion of the author and does not necessarily represent the
official position of the NFPA or its Technical Committees. In addition,
this correspondence is neither intended, nor should it be relied upon,
to provide professional consultation or services
It should be noted that the above is my opinion as a member of the NFPA
Automatic Sprinkler System Hanging and Bracing Committee and the Hanging
and Bracing for Fire Suppression Systems Committee in accordance with
the NFPA Regulations Governing Committee Projects and should therefore
not be considered, nor relied upon, as the official position of the NFPA
or its Committees
*
On 10/26/2021 7:12 AM, Matt Grise via Sprinklerforum wrote:
I am looking at selecting concrete anchors for a project with seismic
requirements, and I am curious about the various approvals that are out there.
I have seen various types of approvals: ACI 355.2; ACI 318; ICC-ESR; UL
203/203A; FM approved, UL listed
As far as I can tell - the ACI and ICC-ESR approvals meet NFPA requirements, but does
anyone know about the others? Some product websites claim that they can be used in
seismic areas since they are tested in accordance with UL 203. Many are FM approved, but
the FM approval just says "approved for supporting pipe hangers" and not much
else. Does anyone know if those listings actually meet the code intent?
Thanks!
Matt
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org