Sean,

While that section does say "small rooms" in the 2019 edition, it was not
the committee's intent to only allow different K-factor sprinklers in light
hazard occupancies less than 800 sq. ft based on the definition. The
language was updated for the 2022 edition to clarify that intent:

28.2.4.9.3*
Sprinklers with different K-factors shall be acceptable for specific uses,
such as exposure protection, small enclosures, smaller portions of a room,
or directional discharge, where an adjacent sprinkler does not need to
discharge as much water.

Committee Statement: This change combined with better alignment of Annex
material is attempting to emphasize that the identified applications are
just some of the examples where different K-factor sizes can be applied.
Particularly, it needs to show that this can occur within the same room
without there being a change in orientation between the different
sprinklers. Additionally, the reference to a Small Room is misleading since
an area of up to 800 sf is not a justification for changing K-factors (nor
is the restriction to light hazard applicable).

As long as the change in K-Factor is not for hydraulic balancing, it is
permitted.

Thanks,
Kevin

The above is my opinion and has not been processed as a formal
interpretation in accordance with the NFPA Regulations Governing Committee
Projects. This is provided with the understanding that the AFSA assumes no
liability for this opinion or actions taken on it and they are not to be
considered the official position of the NFPA or its technical committees.
AFSA cannot provide design or consulting engineering services, and this
opinion should therefore not be considered, nor relied upon, as such.


Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE

Coordinator, Engineering and Technical Services

American Fire Sprinkler Association

[email protected]

214-349-5971


On Fri, Oct 29, 2021 at 10:09 AM Sean Lockyer via Sprinklerforum <
[email protected]> wrote:

> NFPA 13 generally discourages the use of mixing K-Factors in a system;
> however, the mixing of K-Factors is allowed in certain circumstances,
> namely in section 23.4.4.9.3 where it allows such use for small rooms and
> enclosures. In a self-storage facility, the small 5' x 5' storage units
> would not be considered "small rooms" as they are not light hazard (once
> again, per the strict definition as layed out in chapter 3). However, would
> you be able to consider the small units as enclosures since they are
> completely separate rooms from the other, larger self-storage units ?
>
>             Sean Lockyer
>             Project Designer                            6817 N. Orange
> Blossom Trail
>             Cell    386-337-1078                             Orlando,
> Florida 32810
>             [email protected]             Phone:    407-816-9101
>             www.AITLifeSafety.com
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to