Subject: Re: Dry System Size

For the record, I directed the development of the FDT program during my tenure 
as VP of marketing with Tyco Fire Products.
The listing of the program was based on its accuracy in duplicating the 
delivery times of many different arrangements that had been configured and 
timed by the old Central Sprinkler group (my recollection is that the program 
demonstrated its accuracy for nearly forty tests that had been conducted).  All 
of the test arrangements were done with 'tree' configiurations.  No 'looped' 
systems had been included in the Central testing, and, thus, there were zero 
results against which the accuracy of the program could be tested.  The program 
is capable of calculating a simple looped system, but the listings that were 
granted were based on the tree testing and the accuracy of the program results.
Hope that this answers your question regarding the listings or lack thereof for 
looped systems.
A happily retired Tom Prymak 