Mike-
I agree with the cost angle. Thanks for your time and the references you 
provided.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Mike Morey via Sprinklerforum
Sent: Monday, November 08, 2021 10:27 AM
To: [email protected]
Cc: Mike Morey <[email protected]>
Subject: RE: Best Common Practices

Pretty sure that one was entirely dictated by cost.  We've done the opposite on 
occasion when it made sense.  See it a lot in cold storage due to pitch 
requirements when the structural runs up the slope, typically those can be done 
with expanding fasteners though so it's not that big of a deal.  You might hit 
him with some NFPA figures as most follow that "standard.  From 2019 edition of 
13: A.10.2.6.1.4.4, A14.2.8.2.3, A.17.4.3.4

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 /  cell 
260.417.0625 /  fax 260.487.7991 email [email protected]



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Brian Harris via Sprinklerforum
Sent: Monday, November 8, 2021 10:22 AM
To: [email protected]
Cc: Brian Harris <[email protected]>
Subject: Best Common Practices

 
BE ADVISED - This email originated outside EMCOR. 
 

I know it's common practice to run Mains parallel with the structure and 
Branchlines perpendicular to it but is that written anywhere? I actually have 
an architect that would like to see it in writing...

Brian Harris, CET
BVS Systems Inc.
Design Manager
https://urldefense.com/v3/__http://bvssystemsinc.com__;!!FaxH778!O3W2qjDcTiChMdxtu4ebp9RR_SeFZ2dWgBoOKi4p26xDCJEjLDjMJXKt6WClAH7a$
 
<https://urldefense.com/v3/__http://bvssystemsinc.com/__;!!FaxH778!O3W2qjDcTiChMdxtu4ebp9RR_SeFZ2dWgBoOKi4p26xDCJEjLDjMJXKt6bSYzGiw$
 >
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!O3W2qjDcTiChMdxtu4ebp9RR_SeFZ2dWgBoOKi4p26xDCJEjLDjMJXKt6cMYj_7a$
 

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to