Copy.  Was installed/designed to 2013 Edition.  Central station reporting is 
not operational.  Thanks for all.

Byron

________________________________
From: Sprinklerforum <[email protected]> on behalf 
of John Denhardt via Sprinklerforum <[email protected]>
Sent: Thursday, November 18, 2021 11:23 PM
To: [email protected] 
<[email protected]>
Cc: John Denhardt <[email protected]>
Subject: Re: Fire Pump Shutdown

Keep in mind the following from UFC 3-600-01 (8 AUGUST 2016, CHANGE 5, 14
SEPTEMBER 2020)

9.5.3 Pump Start and Shutdown.


9.5.3.1 Fire pumps must be arranged to start automatically.


9.5.3.2 Fire pumps must be arranged to automatically shut down after
reaching the

stop pressure and the expiration of \3\the minimum run time determined by
NFPA 20/3/.

Stop pressure must be at least 5 psi below maximum churn pressure at the
lowest

available static pressure.

Note: The lowest available static pressure should be utilized in
determining churn

pressure so that the stop pressure can be achieved with low pressure. The 5
psi

differential is used to allow for gauge error.\2\


9.5.3 /2/Fire pump activation (run) must transmit an alarm condition to the

Installation receiving station, or remote receiving station, but not
activate the Facility

notification appliance


While I understand what the above states, my personal opinion is to have
the fire pump operating anytime a sprinkler is operating.  We do not want
to short cycle the fire pump.  My suggestion is always for manual shut-down
unless the site is unmanned and response to the site would take
considerable time..  A properly designed and maintained fire pump system
can operate at churn or near churn conditions for a lengthy time with no
issues.

We all know fire pump systems are maintained in full accordance with NFPA
25 and the manufacturer's recommendations.

*The above is my opinion and has not been processed as a formal
interpretation in accordance with the NFPA Regulations Governing Committee
Projects. This is provided with the understanding that the AFSA assumes no
liability for this opinion or actions taken on it and they are not to be
considered the official position of the **AFSA, and/or NFPA or its
technical committees.**AFSA cannot provide design or consulting engineering
services, and this opinion should therefore not be considered, nor relied
upon, as such.*

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://emea01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Ffiresprinkler.org%2F&amp;data=04%7C01%7C%7C0a707228b52e462e7bdf08d9aad158c1%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728638381947890%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=rjKLeILFmyWmuIM8bD95k3UXngPM8uj2FE9IGXC9n28%3D&amp;reserved=0>
<https://emea01.safelinks.protection.outlook.com/?url=https%3A%2F%2Ftwitter.com%2Fafsa%2Fstatus%2F1039528345367732224&amp;data=04%7C01%7C%7C0a707228b52e462e7bdf08d9aad158c1%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728638381947890%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=zT7ptnwbwFl7eJfSyLVF%2Fis24%2FWI5hbgHshQxlnwNTk%3D&amp;reserved=0>
<https://emea01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fcompany%2Famerican-fire-sprinkler-association-afsa-%2F&amp;data=04%7C01%7C%7C0a707228b52e462e7bdf08d9aad158c1%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728638381957884%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=jiiRnKLqdDJ3XknRc9xjZ4pvPLlGwnpmycsqbf%2Bvojw%3D&amp;reserved=0>
   
<https://emea01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.instagram.com%2Ffiresprinklerorg%2F&amp;data=04%7C01%7C%7C0a707228b52e462e7bdf08d9aad158c1%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728638381957884%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=XHFN%2FUfqceQPLDHJp2U8h%2FGCn%2Bum9nRVpV7x5TVgfZ8%3D&amp;reserved=0>

*Our members are at the heart of everything we do.*


*Are you a member with a technical question? *

Don't forget one of the most valuable resources that American Fire
Sprinkler Association provides is technical reviews from our Engineering &
Technical Services Department. It’s like having an FPE on your staff. Visit
https://emea01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.firesprinkler.org%2Finterp&amp;data=04%7C01%7C%7C0a707228b52e462e7bdf08d9aad158c1%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728638381957884%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=RFc1f7mkX64itM%2F0oAQsSnKV77J7pHpJZSOMibMgYDk%3D&amp;reserved=0
<https://emea01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.firesprinkler.org%2FWWW%2FContacts%2FSign_In.aspx%3FWebsiteKey%3D3dff22a3-0306-479c-bccc-7aa1986c8ada%26LoginRedirect%3Dtrue%26returnurl%3D%2FWWW%2FTechnical_Services%2FInformal_Interpretations%2FWWW%2FInformal_Interpret%2FMember_View.aspx%3Fhkey%3D8023e65f-a2ad-4465-9920-0f9313a07324&amp;data=04%7C01%7C%7C0a707228b52e462e7bdf08d9aad158c1%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728638381957884%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=KrUDE8LwjqoTx9irePmTSD00XOllnxTPcchJIIhgGBo%3D&amp;reserved=0>
to
submit a question today!



On Thu, Nov 18, 2021 at 3:13 PM BF Blake via Sprinklerforum <
[email protected]> wrote:

> Thanks John, 100% with you.
> Byron, Poland.
>
>
> ________________________________
> From: Sprinklerforum <[email protected]> on
> behalf of John Denhardt via Sprinklerforum <
> [email protected]>
> Sent: Thursday, November 18, 2021 11:11 PM
> To: [email protected] <
> [email protected]>
> Cc: John Denhardt <[email protected]>
> Subject: Re: Fire Pump Shutdown
>
> To me, the intent is to have the fire pump operating anytime a sprinkler is
> operating.  We do not want to short cycle the fire pump.  My suggestion is
> always for manual shut-down unless the site is unmanned and response to
> Technical he site would take considerable time..  A properly designed and
> maintained fire pump system can operate at churn or near churn conditions
> for a lengthy time with no issues.
>
> *The above is my opinion and has not been processed as a formal
> interpretation in accordance with the NFPA Regulations Governing Committee
> Projects. This is provided with the understanding that the AFSA assumes no
> liability for this opinion or actions taken on it and they are not to be
> considered the official position of the **AFSA, and/or NFPA or its
> technical committees.**AFSA cannot provide design or consulting engineering
> services, and this opinion should therefore not be considered, nor relied
> upon, as such.*
>
> Thanks,
> John
>
> John August Denhardt, PE
> *Vice President, Engineering and Technical Services*
>
> *American Fire Sprinkler Association*
> m: p: 301-343-1457
> 214-349-5965 ext 121
> w: firesprinkler.org
> <
> https://emea01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Ffiresprinkler.org%2F&amp;data=04%7C01%7C%7C0a707228b52e462e7bdf08d9aad158c1%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728638381957884%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=jtxlYwalm4aF6nZhdCMwrsu1jCr3gjeg6JnKQe3tJW0%3D&amp;reserved=0
> >
> <
> https://emea01.safelinks.protection.outlook.com/?url=https%3A%2F%2Ftwitter.com%2Fafsa%2Fstatus%2F1039528345367732224&amp;data=04%7C01%7C%7C0a707228b52e462e7bdf08d9aad158c1%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728638381957884%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=8i%2B3RDZgoHQ7HmS6cIq4eHW1y0Lr00FWXRDA8IunoMk%3D&amp;reserved=0
> >
> <
> https://emea01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fcompany%2Famerican-fire-sprinkler-association-afsa-%2F&amp;data=04%7C01%7C%7C0a707228b52e462e7bdf08d9aad158c1%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728638381957884%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=jiiRnKLqdDJ3XknRc9xjZ4pvPLlGwnpmycsqbf%2Bvojw%3D&amp;reserved=0
> >
>    <
> https://emea01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.instagram.com%2Ffiresprinklerorg%2F&amp;data=04%7C01%7C%7C0a707228b52e462e7bdf08d9aad158c1%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728638381957884%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=XHFN%2FUfqceQPLDHJp2U8h%2FGCn%2Bum9nRVpV7x5TVgfZ8%3D&amp;reserved=0
> >
>
> *Our members are at the heart of everything we do.*
>
>
> *Are you a member with a technical question? *
>
> Don't forget one of the most valuable resources that American Fire
> Sprinkler Association provides is technical reviews from our Engineering &
> Technical Services Department. It’s like having an FPE on your staff. Visit
>
> https://emea01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.firesprinkler.org%2Finterp&amp;data=04%7C01%7C%7C0a707228b52e462e7bdf08d9aad158c1%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728638381957884%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=RFc1f7mkX64itM%2F0oAQsSnKV77J7pHpJZSOMibMgYDk%3D&amp;reserved=0
> <
> https://emea01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.firesprinkler.org%2FWWW%2FContacts%2FSign_In.aspx%3FWebsiteKey%3D3dff22a3-0306-479c-bccc-7aa1986c8ada%26LoginRedirect%3Dtrue%26returnurl%3D%2FWWW%2FTechnical_Services%2FInformal_Interpretations%2FWWW%2FInformal_Interpret%2FMember_View.aspx%3Fhkey%3D8023e65f-a2ad-4465-9920-0f9313a07324&amp;data=04%7C01%7C%7C0a707228b52e462e7bdf08d9aad158c1%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728638381957884%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=KrUDE8LwjqoTx9irePmTSD00XOllnxTPcchJIIhgGBo%3D&amp;reserved=0
> >
> to
> submit a question today!
>
>
> On Thu, Nov 18, 2021 at 2:27 PM BF Blake via Sprinklerforum <
> [email protected]> wrote:
>
> > Greetings Forum Members
> >
> > Do we believe it is the intent of NFPA 20 TC is  for 10 minute automatic
> > shut down (when enabled) of fire pumps to apply only during churn (e.g.
> > dead head, closed loop, testing) conditions or to any condition to
> include
> > sprinkler flow (e.g. 1/2" 5.6K ITC flow)?
> >
> > Is the intent to protect the fire pump from "burn out"?  Is the intent to
> > run pumps to failure (destruction) or is the intent, with 10 minute auto
> > shut down, where permitted, to attempt to preserve the pump?
> >
> > Thanks
> >
> > Byron
> > NATO Facility
> > UFC Criteria 03-600-01 (2013) Applicable
> > Słupsk, Pomorskie, Poland
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> https://emea01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C01%7C%7C0a707228b52e462e7bdf08d9aad158c1%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728638381957884%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=W7KuNdZjnO1SyWduGlmNDTne3C%2FC1OTE%2FgUVUico%2FZM%3D&amp;reserved=0
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://emea01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C01%7C%7C0a707228b52e462e7bdf08d9aad158c1%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728638381967876%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=Y3fIUnR4j0DyoL3cSkTZTmtNyBNZSKmbQt%2FOv0axB7k%3D&amp;reserved=0
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://emea01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C01%7C%7C0a707228b52e462e7bdf08d9aad158c1%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728638381967876%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=Y3fIUnR4j0DyoL3cSkTZTmtNyBNZSKmbQt%2FOv0axB7k%3D&amp;reserved=0
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://emea01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C01%7C%7C0a707228b52e462e7bdf08d9aad158c1%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728638381967876%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=Y3fIUnR4j0DyoL3cSkTZTmtNyBNZSKmbQt%2FOv0axB7k%3D&amp;reserved=0
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to