If project is referencing the IFC I would recommend Chapter 57, which 
references back to Chapter 50. If you end up at 5004.2.2.3 you come up with 20 
minutes. nb room or design area text.

If you were calling me as a plan reviewer working with an architect there would 
be a code analysis agreed to the would call for spill control and secondary 
containment, with criteria, or confirmation that code required secondary 
containment would not be triggered. 

We had a couple projects that had 60 minutes, driven by insurer.

Best.

Bruce Verhei 
> On 12/14/2021 4:08 PM James Crawford via Sprinklerforum 
> <sprinklerforum@lists.firesprinkler.org> wrote:
> 
>  
> Hope some can help, I seem to remember there was a time frame of the 
> sprinkler demand plus largest container in order to figure out the amount of 
> containment requires for a flammable storage room, but cannot seem to find it.
> 
> Can only find the 20 minutes for plastic containers.
> 
> Can someone point me in the right direction.
> 
> Thank You
> 