Thanks all, Below is the paragraph in NATSPEC:
0833 SPRINKLERS 1 GENERAL 1.1 RESPONSIBILITIES General General: Provide automatic fire sprinklers, as documented. 1.2 DESIGN General Standard: To AS 2118.1. 1.3 CROSS REFERENCES General Requirement: Conform to the following: - 0171 General requirements. - 0801 Hydraulic systems. - 0816 Tanks. 1.4 STANDARDS General General requirements: To AS 2118.1. Drencher (wall wetting) system: To AS 2118.2. Deluge system: To AS 2118.3. Residential system: For accommodation buildings 4 storeys or less in height to AS 2118.4. Combined sprinkler and hydrant systems: To AS 2118.6. ......... 2.2 STEEL PIPING Fittings General: Wall thickness to match that of the pipe. Screwed fittings: Heavy pattern, low carbon steel suitable for making screwed joints to AS ISO 7.1. Welded pipe construction: Provide butt-weld flanges. Pipe bends: To AS 4041. Elbows: - < DN 50: Screwed type. - ≥ DN 50: Either welded or segmented roll-grooved type. Tees: - < DN 50: Screwed type. - ≥ DN 50: Either welded or roll-grooved type. Mechanical roll-grooved fittings: Provide only in accessible locations, in sprinkler-protected areas. Flanges: To AS 2129. Bolts for flanges: Carbon steel to AS 2129 Appendix C. - Finish: Zinc-plated in non-corrosive environments; otherwise a protective finish with equivalent corrosion resistance to, and compatible with, the flange. Thread sealing: Seal the threads of screwed connections with degreased PTFE tape or hemp with a thread sealing compound. Regards, Le Vu Phong -----Original Message----- From: Sprinklerforum <[email protected]> On Behalf Of Bob Caputo via Sprinklerforum Sent: Wednesday, December 15, 2021 1:04 PM To: [email protected] Cc: Bob Caputo <[email protected]> Subject: Re: Mechanical roll-grooved fittings for fire pipe NFPA 13 does provide rules for grooved piping. These rules are copied from the 2016 edition, so the current edition section numbers will be different. 6.5.3.1* Pipe, fittings, valves, and devices to be joined with grooved couplings shall contain cut, rolled, or cast grooves that are dimensionally compatible with the couplings. 6.5.3.1.1* Pipe, fittings, valves, devices, and couplings that conform with or are listed in compliance with standardized groove specifications shall be considered compatible. 6.5.3.1.2 Other groove dimensions and grooving methods shall be acceptable in accordance with 6.5.5.1. 6.5.3.2 Grooved couplings, including gaskets used on dry pipe, preaction, and deluge systems, shall be listed for dry service. Coupling manufacturers are required to observe these dimensionally compatible specifications so that any manufacturer’s couplings or fittings will work with any other brand. As always, the opinions expressed herein are my personal opinions and may not be considered as the opinion of NFPA or its committees. This opinion should not be considered or used as consultation services. Bob Caputo, President AFSA On Wed, Dec 15, 2021 at 8:55 AM Jamie Seidl via Sprinklerforum < [email protected]> wrote: > You are going to need to cite a specific section, and preferably > provide a link to said section, otherwise we will not know what you're > referencing. > The link you provided takes you to a gateway page, and I don't think > there are many of us that have the time to find roll groove specs in > what appears to be a "spec book" web page. > Can you give us a section you have in question? > > -Jamie Seidl > > On Tue, Dec 14, 2021 at 11:28 PM Phong - Indochine Engineering via > Sprinklerforum <[email protected]> wrote: > > > Dear All, > > > > NATSPEC in Australia specify the application of mechanical > > roll-grooved > > fittings: Provide only in sprinkler-protected areas. > > https://www.natspec.com.au/ > > > > I wonder why and if NFPA has a similar rule? > > > > Thanks for discussing. > > > > Regards, > > Le Vu Phong > > Mobile: +84 (0) 902 363 525 > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org > -- Bob Caputo, CFPS *President* *American Fire Sprinkler Association* p: 214-349-5965 ext124 w: firesprinkler.org <https://www.facebook.com/firesprinkler.org/> <https://twitter.com/afsa/status/1039528345367732224> <https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/> <https://www.instagram.com/firesprinklerorg/> *Train a safer, more efficient workforce.* By enrolling your employees in the AFSA Apprenticeship Training Series for Sprinkler Fitters <https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>, you will reap the benefits of a qualified, professional installation crew. Well-trained employees will work smarter, increasing your company's productivity and, in turn, its profits. Learn more <https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149> . _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org