Allan,

I am not sure I follow how you are applying the OH spacing rules to ESFR 
listings. These sprinklers are still covering 100sf each on average, and the 
spacing adjustment is spelled out specifically in NFPA 13. The discharge is not 
designated by coverage area, it never goes up or down depending on the head 
spacing.

I agree that the shorter gap gets more water than the longer gap, but it seems 
that the longer gap has been found to perform ok?

Matt 


-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of AKS-Gmail-IMAP via Sprinklerforum
Sent: Tuesday, January 18, 2022 3:15 PM
To: [email protected]
Cc: AKS-Gmail-IMAP <[email protected]>
Subject: Re: ESFR obstruction shift

How I see this, when the distance between sprinklers varies, the more demanding 
distance is what drives the required minimum discharge pressure. The shorter 
distance gets over discharged but the longer distance gets the application 
called for in the design. So these sprinklers need to be pressurized for 110 sf 
operational area, not 100 sf. I think you are in trouble if there is a 100 sf 
limitation imposed somewhere that is not countered and accepted by using a 
hydraulic design for 110 sf per sprinkler.

A somewhat similar, but perhaps more defendable, condition to this occurs when 
two rooms each having 130 sf/sprinkler designs, but as 10 x 13 in one room and 
13 x 10 in the other room, have the dividing wall between the rooms removed. 
The design in each room worked on its own, including up to its wall, but now 
the design is technically 11.5 x 13 where the wall used to be. It is defendable 
when one considers each sprinkler as having its own operational area, but that 
concept is not normally accepted and has been shot down here without 
discussion.   

Allan Seidel

> On Jan 18, 2022, at 10:50 AM, Kyle.Montgomery via Sprinklerforum 
> <[email protected]> wrote:
> 
> Matt,
> 
> I haven't dealt with that situation in real life, but have in theory had 
> several conversations about it. I am in agreement with you that this should 
> be allowable per the code language. You never exceed 110 s.f. and the average 
> ACTUAL FLOOR AREA (not SxL) does not exceed 100 s.f.
> 
> -Kyle M
> 
> -----Original Message-----
> From: Sprinklerforum <[email protected]> 
> On Behalf Of Matt Grise via Sprinklerforum
> Sent: Tuesday, January 18, 2022 8:22 AM
> To: [email protected]
> Cc: Matt Grise <[email protected]>
> Subject: [EXTERNAL] RE: ESFR obstruction shift
> 
> No - since we are moving along the line, when one space goes from 10 to 11, 
> the space on the other side goes from 10' to 9'
> 
> Matt
> 
> 
> -----Original Message-----
> From: Sprinklerforum <[email protected]> 
> On Behalf Of Matthew J Willis via Sprinklerforum
> Sent: Tuesday, January 18, 2022 9:00 AM
> To: [email protected]
> Cc: Matthew J Willis <[email protected]>
> Subject: RE: ESFR obstruction shift
> 
> Are you not creating a 10x11 situation since you are moving every other 
> sprinkler?
> 
> If so, you may be violating the 100 sq ft per average requirement for moved 
> and adjacent?
> 
> R/
> Matt
> 
> -----Original Message-----
> From: Sprinklerforum <[email protected]> 
> On Behalf Of Matt Grise via Sprinklerforum
> Sent: Tuesday, January 18, 2022 6:00 AM
> To: [email protected]
> Cc: Matt Grise <[email protected]>
> Subject: ESFR obstruction shift
> 
> I am looking at a warehouse layout where we can get a very nice head pattern 
> by laying the heads out 10ft by 10ft, and then shifting the ones that land 
> near joists 1ft along the line as allowed by NFPA 13.
> 
> The only issue is that we have to shift every other head. Making a 9ft - 11ft 
> pattern along the branch line. As far as I can tell, this meets the letter of 
> the code, but it seems like a stretch.
> 
> Has anyone come across a similar situation where so many heads needed to be 
> shifted to avoid roof structures?
> 
> Matt
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http
> *3a*2f*2flists.firesprinkler.org*2flistinfo.cgi*2fsprinklerforum-fires
> prinkler.org&c=E,1,l1exGGqk0cDcPNoSdqRWtD1YmZdqStCzx0CUF-Olhi1rqB9Iz8F
> n6d7eBTNXNMfF8T-7GZY94qom2OweTyV4Gyin1hiL-CJ82tDF4yhwF7g0ofhpr4fwsNalR
> ZM,&typo=1__;JSUlJSU!!Ba8_KKAT!eogk1pEssHmJtaZHhoNM1xMOrahW4a40OEoiC7x
> HQPIDjpwV0fnvj8Sfjpv8d1bFGzI$ 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http
> *3a*2f*2flists.firesprinkler.org*2flistinfo.cgi*2fsprinklerforum-fires
> prinkler.org&c=E,1,faagUYTvRqNofSbZjC709kxTbRDQVTelhUkbtQ0AWq4V349KeRL
> ZVnCRia1Vjt6yQqBjB_beLshOylNEy-3N0UIJJJFKTWvWeUpRcWUx-0A,&typo=1__;JSU
> lJSU!!Ba8_KKAT!eogk1pEssHmJtaZHhoNM1xMOrahW4a40OEoiC7xHQPIDjpwV0fnvj8S
> fjpv8sH-n2sk$ _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cg
> i/sprinklerforum-firesprinkler.org__;!!Ba8_KKAT!eogk1pEssHmJtaZHhoNM1x
> MOrahW4a40OEoiC7xHQPIDjpwV0fnvj8Sfjpv8Su2SCv4$
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler
> .org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,TGO-isVpE
> kR7verVmX9CHBUEQ1Lcp5j5D7Btkw7ILCxVbpg47Pe0yvBKBrABRbyXdPfv8yRcHjteSSZ
> QGsrystfIg-BxSH3iUDKwGtSQXk1luhz6XVhYgfA,&typo=1

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler.org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,rN2HWC9lSUrDmEpsEmRlNns6M4ON9nIKNoaxYVBhpDe9Au9EXF6eRUvtBqhKsAKTuCAMDSkqtBUNbwCsyhGy-iJcpehhMCnl7QMJz2J-CJI,&typo=1
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to