I've got a storeroom, ceiling is open to structure.  The roof structure is solid wood joists, which are fully insulated between each joist.

We have installed standard spray upright sprinklers with the deflectors approx 8-10 inches below the bottom of the joist/insulation.

In my mind, this is unobstructed construction, because per "A.8.5.4.1 Batt insulation creates an effective thermal barrier and can be considered the ceiling/roof deck when determining distances between deflector and ceiling."  Chapter 3 defines Obstructed Construction "Panel construction and other construction where beams, trusses, or other members impede heat flow or water distribution in a manner that materially affects the ability of the sprinkler to control or suppress a fire".

Now that I look at this again, I'm thinking I am wrong and should be obstructed construction because although the batt insulation creates a thermal barrier (similar to a smooth ceiling) the structure is still the same, so I would need to keep my upright sprinklers max 6-inches below the bottom of structure?

Would appreciate input from the group.