Thanks for the ammo Mike!

Taylor Schumacher CET
J-Berd Mechanical/Security Fire Sprinkler/Berd Electric
1 Industrial Blvd | Sauk Rapids, MN 56379
Office: 320.656.0847 | Direct: 320.640.7050



-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Mike Morey via Sprinklerforum
Sent: Friday, February 18, 2022 7:15 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Mike Morey <mmo...@shambaugh.com>
Subject: RE: Fire Sprinkler Valve Clearance

NFPA 1 (2018), if enforceable:
13.1.5  A minimum 36 in. (915 mm) of clear space shall be maintained to permit 
access to and operation of fire protection equipment, fire department inlet 
connections, or fire protection system control valves. The fire department 
shall not be deterred or hindered from gaining immediate access to fire 
protection equipment.

IFC simply states you must provide clear space in accordance with manufacturer 
requirements and to be able to maintain etc.

If someone's being a pain about space you could probably get the manufacturer 
to say 3' in an email and then point them to that IFC requirement.  It's 
901.4.6 in 2018.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 /  cell 
260.417.0625 /  fax 260.487.7991 email mmo...@shambaugh.com



-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Taylor Schumacher via Sprinklerforum
Sent: Friday, February 18, 2022 7:48 AM
To: 'sprinklerforum@lists.firesprinkler.org' 
<sprinklerforum@lists.firesprinkler.org>
Cc: Taylor Schumacher <tay...@sfsprinkler.com>
Subject: Fire Sprinkler Valve Clearance

 
BE ADVISED - This email originated outside EMCOR. 
 

I have always told people that sprinkler valves require 36" of clearance in 
front of them. Now, being challenged, I don't know where I've come up with this 
from. Is there a minimum clearance in the codes/standards?


Taylor Schumacher CET
J-Berd Mechanical/Security Fire Sprinkler/Berd 
Electric<https://urldefense.com/v3/__http://www.j-berd.com/__;!!FaxH778!M5ec-xmyV6jql01npM72TYgPVC23WS2eRVTYUI7YMO_P3uk4QgIcgTlVUErvXEJ4$
 >
1 Industrial Blvd | Sauk Rapids, MN 56379
Office: 320.656.0847 | Direct: 320.640.7050



_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!M5ec-xmyV6jql01npM72TYgPVC23WS2eRVTYUI7YMO_P3uk4QgIcgTlVUC5cxbZZ$
 

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to