Does anyone have any idea where these engineers come up with the velocity 
limits?  We have one that they are requiring a 10 PSI margin (not an issue 
since AHJ requires 20%), but also limiting velocity to FOURTEEN fps.  There has 
never been a limit in NFPA 13.  The velocity that we determine is only based on 
a demand calc.  The water supply doesn't know to reduce flow so that a 10 psi 
margin is maintained.  If a single sprinkler activates, that 1" arm over is 
going to see far greater than 14 fps.

It really just baffles me how this criteria has become so ingrained in the 
engineering culture.

Please rate our customer 
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>

Travis Mack, CFPS, CWBSP, RME-G, COC, SET
Senior Engineering Manager
MFP Design
480-505-9271 ext. 700 C: 480-272-2471
[email protected]<mailto:[email protected]>
www.mfpdesign.com<http://www.mfpdesign.com>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>