I have a question on this table. If you go to the height column for 22ft to 25ft, commodity class I, non-encapsulated, 8' aisles it recommends to use figure 21.4.1.2(a) curves B and D. When I read the descriptions for these curves it appears that they are in actuality the wrong curves and I should be looking at curves A and C. Is this a typo in the code as I suspect or am I misunderstanding the intent here? Thank you, Chris Dorn
For reference: A - Single- or double-row racks with 8 ft (2.4 m) aisles and high-temperature ceiling sprinklers B - Single- or double-row racks with 4 ft (1.2 m) aisles and high-temperature ceiling sprinklers C - Single- or double-row racks with 8 ft (2.4 m) aisles and ordinary-temperature ceiling sprinklers D - Single- or double-row racks with 4 ft (1.2 m) aisles and ordinary-temperature ceiling sprinklers [cid:[email protected]]
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]