I have a question on this table. If you go to the height column for 22ft to 
25ft, commodity class I, non-encapsulated, 8' aisles it recommends to use 
figure 21.4.1.2(a) curves B and D. When I read the descriptions for these 
curves it appears that they are in actuality the wrong curves and I should be 
looking at curves A and C. Is this a typo in the code as I suspect or am I 
misunderstanding the intent here?
Thank you,
Chris Dorn

For reference:

A - Single- or double-row racks
with 8 ft (2.4 m) aisles
and high-temperature
ceiling sprinklers
B - Single- or double-row racks
with 4 ft (1.2 m) aisles
and high-temperature
ceiling sprinklers
C - Single- or double-row racks
with 8 ft (2.4 m) aisles
and ordinary-temperature
ceiling sprinklers
D - Single- or double-row racks
with 4 ft (1.2 m) aisles
and ordinary-temperature
ceiling sprinklers