It’s never been allowed, I have however seen an engineer who didn’t know
better design a cold attic gridded to just 1500sqft.
My guess would be this is a similar situation, engineer did understand the
requirements for dry systems and designed like a regular wet system.

On Wed, Sep 7, 2022 at 3:29 PM James Crawford <jcrawf...@phaserfire.ca>
wrote:

> Looking for input
>
>
>
> Just did a site review on a 1984 building and they have 2 gridded dry
> systems in one of their storage canopies.
>
>
>
> Were they ever allowed to do gridded dry system, I know the NFPA 313
> (1989) says no gridded dry system but it is not in the 1978 edition.
>
>
>
> Thank You
>
>
>