A couple of quick thoughts from my perspective. 1. If the firewater at the facility is not monitored or using it for any other purpose would essentially be stealing. 2. You are cross connecting two different water systems. I would make sure that you follow all proper cross connection requirements put in place by the local water purveyor accordance with NFPA and the a ASSE. 3. You will have to have something in place to stop the flow of water to the process piping upon activation of the fire sprinkler system. Another option would be to determine the maximum GPM required by the process piping and account for it in your hydraulic calculations for the sprinkler system.
Chris Dorn Christopher Dorn Dorn Fire Protection LLC 4132 Dumont Street #4 Cincinnati, Ohio 45226 (513) 295-2499 On Sep 9, 2022, at 2:17 PM, Bobby Welch <[email protected]> wrote: Is there a code that does not allow a plants processing water to be connected to the sprinkler system in case the plants processing water supply goes down? im looking for a code that does not allow the water in a sprinkler system to be used for other things including a plants processing water supply. Bobby Welch | Sprinkler Systems Designer KOORSEN FIRE & SECURITY 3577 Concorde Rd, Vandalia, OH 45377 P 937.641.8403 | Ext. 0318 | M 937.594.8457 [email protected]<mailto:[email protected]> | www.koorsen.com<http://www.koorsen.com> 24x7x365 Service: 937.660.7050 | [email protected] _________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]