A couple of quick thoughts from my perspective.
1. If the firewater at the facility is not monitored or using it for any other 
purpose would essentially be stealing.
2. You are cross connecting two different water systems. I would make sure that 
you follow all proper cross connection requirements put in place by the local 
water purveyor accordance with NFPA and the a ASSE.
3. You will have to have something in place to stop the flow of water to the 
process piping upon activation of the fire sprinkler system. Another option 
would be to determine the maximum GPM required by the process piping and 
account for it in your hydraulic calculations for the sprinkler system.

Chris Dorn

Christopher Dorn
Dorn Fire Protection LLC
4132 Dumont Street #4
Cincinnati, Ohio 45226
(513) 295-2499

On Sep 9, 2022, at 2:17 PM, Bobby Welch <[email protected]> wrote:


Is there a code that does not allow a plants processing water to be connected 
to the sprinkler system in case the plants processing water supply goes down? 
im looking for a code that does not allow the water in a sprinkler system to be 
used for other things including a plants processing water supply.

Bobby Welch | Sprinkler Systems Designer
KOORSEN FIRE & SECURITY
3577 Concorde Rd, Vandalia, OH 45377
P 937.641.8403 | Ext. 0318 | M 937.594.8457
[email protected]<mailto:[email protected]> | 
www.koorsen.com<http://www.koorsen.com>

24x7x365 Service: 937.660.7050 | [email protected]

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to