Look at NFPA 13 (2019 ed) FIGURE A.9.5.5.3.1.2   Sprinkler Location Below
Obstruction.

The sprinkler is no longer required to be literally beneath the obstruction.


As long as it is within 3” of the edge and between 1” and 12” below, it
satisfies the requirement for “beneath (under)”.





Thank you,



Bob Knight, CET III

Fire by Knight, LLC

208-318-3057



From: Luis Perea [mailto:[email protected]]
Sent: Wednesday, October 05, 2022 3:19 PM
To: 'Discussion list on issues relating to automatic fire sprinklers'
Subject: [Sprinklerforum] ESFR Sprinkler Under Obstruction



Hi everyone,



Per NFPA-13 i can´t find if it’s mandatory to install a sprinkler under the
HVAC extraction Grill, the size of the duct it is clearly an obstruction and
the option i have been thinking is to install the sprinkler with a baffle
under the grill.

Does anyone know if this is correct or have any other solution?







Thank you.





LRPF









--
This email has been checked for viruses by AVG antivirus software.