NFPA-13 (2016)
8.4.6.3.1 States any solid members over 12" deep must have heads in each bay.
8.4.6.3.2 States to follow minimum spacing rules found in 8.12.2 & 8.12.3. 
Minimum spacing found in 8.12.3.4 calls for 8'.
If I'm working on a warehouse with 22" deep concrete tee's spaced on 6' centers 
how do I keep my head from exploding?