Good morning, 

 

I am working on a Flat Roof, wood frame, single story building.

The membrane roof is insulated above the structure.

5/8" Plywood Roof Deck attached directly to the framing.

Concealed Space is 1'-10" high down to 1'-6" minimum, 11,000 SF

5/8" Gypsum board attached directly to bottom of roof trusses.

 

There is a Noncombustible Concealed Space almost 2'-0" deep where Sprinkler
System piping will be installed with a Finished Ceiling, 5/8" Gyp. Board
suspended on Metal Grid below.

 

Reference NFPA 13, 2022 ed. 9.2.1.15.  9.2.1.15 describes the scenario above
and states that this space below the roof deck shall not require sprinkler
protection. 

 

Would I be correct in not applying sprinklers to this space?

 

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

   117 Old Stage Rd. - Essex Jct., VT. 05452

                 CELL: (802) 373-0638  

              <mailto:[email protected]> [email protected]

 

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to