Using an ESFR sprinkler at 100 GPM for 12 sprinklers may be more of a cost 
savings.

 

Art

 

From: Trillium Fire Sprinkler Design INC <trilliumf...@cwisp.ca> 
Sent: Saturday, December 03, 2022 7:53 AM
To: 'Discussion list on issues relating to automatic fire sprinklers' 
<sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: NFPA 21 VERSUS 22

 

Thanks Ken. Exactly what I was thinking. Just needed clarification.

Troy

 

From: Ken Wagoner <k...@parsleyconsulting.com 
<mailto:k...@parsleyconsulting.com> > 
Sent: December 2, 2022 11:57 AM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: [Sprinklerforum] Re: NFPA 21 VERSUS 22

 

It would be helpful in we were shown where you came up with the references for 
both a density of .325 and an increase of 175%, and perhaps most of all where 
you're directed to "22" (guessing you meant Chapter 22?), as that chapter 
covers the use of CMSA sprinklers.

Table 21.4.1.2.2.1 addresses class II, non-encapsulated storage to 25' height, 
with 8' aisles to figure 21.4.1.2.2.1(b), and curves A or B.  Curve a for high 
temp sprinklers shows 0.325 gpm/ft² over 2,000 ft², which matches what you've 
quoted. If ordinary temp sprinklers are selected (curve B) the density jumps to 
0.375 gpm/ft².

And yes, the density is required to be increased per the graph in Figure 
21.4.1.7.1 to 175% of the values from the curves when the height of storage 
exceeds 20'.  That would result in densities of ± 0.569 for high temps and ± 
0.656 for ordinary temps.
 
I hope this is of some value,

Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181 
Visit the website 
<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>
  

On 12/2/2022 9:23 AM, Trillium Fire Sprinkler Design INC wrote:

I  have a warehouse that has double row rack storage to 25 feet with 8 foot 
aisles. Class II commodity non encapsulated.

 

21 says that .325 density apply the increase of 175%  for  the 25 foot storage. 
Using CMDA sprinklers

 

But then says if using CMDA sprinklers use 22.

 

I am confused!!!!!!!!!

 

Which chapter do I use.

 

 

 

 

 
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org 
<mailto:sprinklerforum-le...@lists.firesprinkler.org> 

 

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to