I did a vertical lift recently that was a parts store. 'Modula' brand. If that is what you have, see FMDS 08-33 for vertical carousel storage. With the configuration we had (non-combustible containers), we ended up in FMDS 08-34 treating as a vertically enclosed ASRS storage unit with storage sprinklers at the top on reduced spacing and an interface for automatic shutdown. The manufacturer had an information page on the places we were permitted to penetrate the top of the unit.
Hope that helps Kind regards [cid:[email protected]]Nicky Marshall Southern Regional Manager PROTECH DESIGN LIMITED Specialist Fire Protection Consultants Mobile Phone: +64 (0)21 433 488 Email: [email protected]<mailto:[email protected]> Web: www.protechdesign.co.nz<http://www.protechdesign.co.nz/> Address:105A Alabama Rd, Redwoodtown, Blenheim 7201, NZ [A close up of a sign Description automatically generated] "I always wondered why somebody doesn't do something about that. Then I realised I was somebody" Lily Tomlin From: Dewayne Martinez <[email protected]> Sent: Saturday, March 18, 2023 5:15 AM To: [email protected] Cc: Dewayne Martinez <[email protected]> Subject: [Sprinklerforum] Vertical lift modules I have a customer who will be installing 2 VLM in there facility. Is there any guidance in NFPA or FM for sprinkler protection in these? All I can find online is for gas systems. Thank you, Dewayne Martinez Fire Protection Design Manager TOTAL Mechanical Building Integrity W234 N2830 Paul Rd. Pewaukee, WI 53072 [email protected]<mailto:[email protected]> Ph: 262-522-7110 Cell: 414-406-5208 http://www.total-mechanical.com/ [cid:[email protected]]
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]