I did a vertical lift recently that was a parts store. 'Modula' brand.
If that is what you have, see FMDS 08-33 for vertical carousel storage.
With the configuration we had (non-combustible containers), we ended up in FMDS 
08-34 treating as a vertically enclosed ASRS storage unit with storage 
sprinklers at the top on reduced spacing and an interface for automatic 
shutdown.
The manufacturer had an information page on the places we were permitted to 
penetrate the top of the unit.

Hope that helps

Kind regards

[cid:[email protected]]Nicky Marshall
Southern Regional Manager

PROTECH DESIGN LIMITED
Specialist Fire Protection Consultants
Mobile Phone: +64 (0)21 433 488  Email: 
[email protected]<mailto:[email protected]>  Web: 
www.protechdesign.co.nz<http://www.protechdesign.co.nz/>
Address:105A Alabama Rd, Redwoodtown, Blenheim 7201, NZ
[A close up of a sign    Description automatically generated]
"I always wondered why somebody doesn't do something about that. Then I 
realised I was somebody" Lily Tomlin

From: Dewayne Martinez <[email protected]>
Sent: Saturday, March 18, 2023 5:15 AM
To: [email protected]
Cc: Dewayne Martinez <[email protected]>
Subject: [Sprinklerforum] Vertical lift modules

I have a customer who will be installing 2 VLM in there facility.  Is there any 
guidance in NFPA or FM for sprinkler protection in these?  All I can find 
online is for gas systems.

Thank you,

Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity

W234 N2830 Paul Rd.
Pewaukee, WI  53072
[email protected]<mailto:[email protected]>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/

[cid:[email protected]]

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to