Thank you Craig, That is perfect. I was conveying this issue to the builder and 
his response was “I have no idea”. Not very helpful…

Chris Dorn


From: Craig Hanson <cra...@wc-3.com>
Sent: Friday, June 30, 2023 9:57 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: Residential Layouts

Chris here is my comment I use when dealing with your situation:

Protection Against Freezing- These are areas that are subject to freezing and 
require that the piping be protected by either direct heating, heat trace, dry 
system or anti-freeze [NFPA 13R 6.7.2.1*]. Although it is the owner’s 
responsibility to maintain areas above 40F, it is the designer’s responsibility 
to ensure the piping is in a conditioned area [NFPA 13(HB): 8.16.4.1.1*]. Using 
of heat trace or other methods need to be approved by the AHJ. Tenting of pipe 
can only be used when the space below the piping is heated, however, an 
alternative is to have a professional engineer supply heat loss calculator that 
the system will not freeze (taking into account of an open garage door) [NFPA 
13: 8.16.4.1.5]. If using a conditioned chase, then it needs to be designed and 
shown on plans.




Craig D. Hanson, CFPS

Senior Fire Plans Examiner

West Coast Code Consultants, Inc. (WC³)

Meridian Satellite Office

C: 253.225.9977 | E: cra...@wc-3.com<mailto:cra...@wc-3.com> | 
www.WC-3.com<https://www.wc-3.com/>

Teaming With Your Community to Make a Difference



On Fri, Jun 30, 2023 at 7:54 AM Chris Dorn 
<chris.d...@dornfireprotection.com<mailto:chris.d...@dornfireprotection.com>> 
wrote:
Interested to see the responses as I’m dealing with this same question. Also 
when the building has breezeways instead of corridors how do you get from one 
block of units to the other without having piping in an unheated area?

Thanks,
Chris Dorn


From: Brian Harris <bhar...@bvssystemsinc.com<mailto:bhar...@bvssystemsinc.com>>
Sent: Friday, June 30, 2023 9:41 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Residential Layouts

I do a residential/apartment project about once every couple years so each time 
it’s like starting from scratch. For you guys that do these a lot which way is 
preferred; running mains and branchlines in joist with pendent heads on the 
first floor and then “bird cage” vertically with sidewalls on the upper floors 
or mains and branchlines all floors with pendants?

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935



_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>