While the standard cannot contemplate every scenario, and you have a unique 
one, you have to look at the intent there.

8.15.7.3 says the meat of the sandwich must be a sprinklered concealed space or 
meet the allowable omissions for non-sprinklered concealed spaces.

You have a concealed space which qualifies you to not require sprinklers there, 
so I think it meets the intended purpose of that omission. Now to check the 
other boxes to omit sprinkler protection below the overhang (storage of 
combustibles, etc.).


Taylor Schumacher

From: Matt Grise <mattgri...@gmail.com>
Sent: Thursday, July 20, 2023 7:28 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] canopy construction


Caution: This email originated from outside your organization. Please take care 
when clicking links or opening attachments.


We have a non-combustible, light hazard building where a steel pan roof deck 
(with some non-combustible architectural finishes on the underside) forms a 
balcony over a patio. The steel roof deck has a drainage slope on top formed 
from combustible rigid insulation that is covered with non-combustible roofing 
material – forming a noncombustible-combustible-noncombustible sandwich. There 
are no exposed combustible materials or combustible concealed spaces since all 
of the materials are in direct contact.

We typically see these considered non-combustible construction and exempt from 
sprinklers per NFPA 13 2016 ed 8.15.7.2, however a plans reviewer has expressed 
concerns that the presence of the combustible middle layer voids the 
‘non-combustible construction’ consideration.

It seems that the code allows for the presence of some combustible materials in 
the assembly based on NFPA 13 2016 ed 8.15.7.3 allowances for combustible 
construction with non-combustible finishes. However, this specific construction 
does not meet any of the specifically listed exemptions.

Has anyone seen anything similar to this?

Matt