We have used brass nipples in the past for similar issues.

On Wed, Aug 9, 2023 at 1:33 PM Eric Rieve <[email protected]> wrote:

>
>
> So, running with this topic a bit. Let’s say this “theoretical” new system
> is a warehouse fab where some ¾” heads need to be raised up a bit for
> proper distance to ceiling due to deeper than expected I-beams. The fun
> question to ask is it ok to use ¾” x 6” stainless steel nipples and ¾”
> stainless steel couplings to raise those heads up? The ¾” weld-o-lets
> aren’t stainless, but the relevant section in NFPA 13 only mentions pipe
> and not fittings. Assuming it calc’s out ok hydraulically of course.
>
>
>
> Eric Rieve
>
> Rieve Fire Protection
>
>
>
> *From:* Travis Mack <[email protected]>
> *Sent:* Wednesday, August 9, 2023 1:53 PM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: 3/4" Nipple
>
>
>
> You ask if it is ever allowed.  That answer is yes.  You can use ¾” CPVC,
> Copper and maybe even a few other types of pipe. Those are just the ones
> that pop into my head initially.  If you are talking black or galvanized
> steel pipe, then no, it is not acceptable in a new system.
>
>
>
>
>
> Travis Mack, SET
>
> *M.E.P.CAD* | Instructor / Support
>
> 181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
>
> www.mepcad.com | *m: 480.547.9348*|* Whatspp: +14805479348*
>
> *Email: [email protected] <[email protected]>*
>
>
>
> *AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD*
>
>
>
> *From:* Brian Harris <[email protected]>
> *Sent:* Wednesday, August 9, 2023 10:49 AM
> *To:* [email protected]
> *Subject:* [Sprinklerforum] 3/4" Nipple
>
>
>
> Is it ever allowed in a *new system* to use a ¾” nipple to a 1” x ¾”
> reducer, then to a 1” Sprig? I say no unless it’s a revamped system.
>
>
>
> *Brian Harris, CET*
>
> BVS Systems Inc.
>
> bvssystemsinc.com
>
> Phone: 704.896.9989
>
> Fax: 704.896.1935
>
>
>
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>


-- 

Greg McGahan

*Genesis Fire Services, LLC*

*4912 Glover Lane. Milton, FL **32570*

*P- 850-637-8535*

*C- 850-712-9555*
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to