True, if your tank is down for maintenance…

That occurs pretty infrequently, I’m sure we all agree.   Like maybe once every 
20 years or so?   We take sprinkler systems in and out of service without any 
special consideration all the time and keep in mind that there are options for 
fire watch, temporary piping arrangements and the FDC to help mitigate 
impairment for the short period of time that the tank might have to be emptied.


The foregoing is my opinion only and does not represent NFPA or the NFPA 14 
Technical Committee, nor intended to serve as an interpretation of the standard.

Protection Design and Consulting
Steve Leyton, President
T  |  619.255.8964 x 102  |  
www.protectiondesign.com<http://www.protectiondesign.com/>
2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108
Fire Protection System Design | Consulting | Planning | Training







From: Travis Mack <t.m...@mepcad.com>
Sent: Monday, September 25, 2023 12:11 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: Standpipe PRV Question

Steve:

I was envisioning that you had your city supply going to the tank and you had 
the full tank.  So if there is activation, you have either city supply or tank 
as back up.  That is no issue.  But if there is no direct bypass around the 
tank, then when your tank is down for maintenance, your entire water supply is 
down for that period.

Maybe I am not perfectly picturing what you are indicating.


Travis Mack, SET
M.E.P.CAD | Instructor / Support
181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348| Whatspp: +14805479348
Email: t.m...@mepcad.com<mailto:t.m...@mepcad.com>

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

From: Steve Leyton 
<st...@protectiondesign.com<mailto:st...@protectiondesign.com>>
Sent: Monday, September 25, 2023 12:05 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: Standpipe PRV Question

Respectfully don’t concur.

The point of the tank is to store a reserve of standpipe water or sprinkler 
water, whichever volume is highest given demand x duration.   This requirement 
is intended to mitigate interruption of the primary water supply (city main) 
due to a cataclysmic seismic event that might damage the service lateral or 
public system.  Assuming it’s sized correctly, you start with a full tank and 
the pump begins drafting and almost immediately, the autofill opens.  We use 6” 
fill lines, so once its open, the fill line will either maintain the tank level 
or augment it.   If at some point the supply to the tank is interrupted, you at 
least have tank water for the calculated duration at full demand.

Even if the public (fill) supply is interrupted before the pump operates, you 
still have a full tank at the start.  Which is the point, to assure an adequate 
water supply for the duration of an activation.  Not two separate (and 
potentially concurrent) water supplies, just a back-up to assure that you have 
one reliable one.   And you won’t have that if you’re drafting just from the 
city main and it gets interrupted, so I think this arrangement is consistent 
with the intent.   And all the AHJ’s out here in Earthquake Country seem to 
agree, as this is a fairly standard arrangement.

The foregoing is my opinion only and does not represent NFPA or the NFPA 14 
Technical Committee, nor intended to serve as an interpretation of the standard.

Protection Design and Consulting
Steve Leyton, President
T  |  619.255.8964 x 102  |  
www.protectiondesign.com<http://www.protectiondesign.com/>
2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108
Fire Protection System Design | Consulting | Planning | Training







From: Travis Mack <t.m...@mepcad.com<mailto:t.m...@mepcad.com>>
Sent: Monday, September 25, 2023 9:47 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: Standpipe PRV Question

In my opinion, that is not dual water supplies. If the tank is down your water 
supply is down. You need one connected to the city and one connected to the 
tank. Yes. It can be quite tough to balance that calc. I’ve had to put a PRV on 
the incoming line so as to basically kill most of the supply pressure.


Travis Mack, SET

M.E.P.CAD |

181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348



AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD



Book appointment time in my calendar

https://calendly.com/t_mack_mepcad

________________________________
From: Micah Davis <micah...@gmail.com<mailto:micah...@gmail.com>>
Sent: Monday, September 25, 2023 9:17:40 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: Standpipe PRV Question

Thank you for the response, Steve!  Does the redundant fill valves for the tank 
satisfy the secondary supply requirement of the IBC without an additional tank? 
 I was interpreting the city main connected to the pump as the primary supply 
and the tank as the secondary supply (or vice versa).  If my interpretation is 
wrong and the tank with redundant fill valves meets BOTH the primary and 
secondary water supply requirements, I can NOT connect the city water main to 
the fire pump, and the problem is solved using your method above.

Am I tracking correctly?

My thought is that if the city main stays connected to the pump and my demand 
calcs and PRV settings are based on the supply from the tank (which I think is 
correct), how do we avoid overpressurization with the added pressure from the 
city?  I'm probably overthinking this somewhere!  That tends to be my M.O.!


Micah Davis

Ferguson Fire Design

micah.da...@ferguson.com<mailto:micah.da...@ferguson.com>


On Mon, Sep 25, 2023 at 12:02 PM Steve Leyton 
<st...@protectiondesign.com<mailto:st...@protectiondesign.com>> wrote:

Micah:

The best way to stabilize the pump discharge pressure and give yourself a 
(nearly) straight line suction pressure curve is to arrange the required 
secondary water supply as a break tank.   Fill the tank with city water 
(recommend to manifold at least one automatic plus one manual fill; in my neck 
of the woods we use two automatic and one manual) and base  your calculations 
on the lowest potential water level in the tank.  We simply use the pump’s 
performance curve as a water supply assuming 0 psi suction head.   Depending on 
water column height, your actual discharge pressure variation will be  ≤ 5 psi, 
unless the tank is uniquely configured and multi-story.





The foregoing is my opinion only and does not represent NFPA or the NFPA 14 
Technical Committee, nor intended to serve as an interpretation of the standard.



Protection Design and Consulting

Steve Leyton, President

T  |  619.255.8964 x 102  |  
www.protectiondesign.com<http://www.protectiondesign.com/>
2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108
Fire Protection System Design | Consulting | Planning | Training















From: Micah Davis <micah...@gmail.com<mailto:micah...@gmail.com>>
Sent: Monday, September 25, 2023 8:55 AM
To: SprinklerForum 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Standpipe PRV Question



Good morning, Forum!



I've got a head-scratcher and am interested in the Forum's collective opinion!  
Important project parameters are as follows.



- 42-story high rise with an automatic standpipe

- Seismic Design Category - C

- IBC 2018

- Fire pump supplied by city water supply

- Secondary supply, as required by IBC 403.3.3, is a tank of adequate size

- 305 psi @ 1000 gpm pump sized based on the feed from tank

- Direct-acting pressure reducing valves on each floor



Here is my issue.  If I base my PRV settings on city supply, I cannot get 100 
psi at the remote valves when calculating tank as supply.  If I base my PRV 
settings on tank supply, I am over 175 psi discharge on the valve when 
calculating city as supply.  If I try to get my settings using the city as 
static and the tank as residual pressures, there is no PRV setting that works.



I have my opinions about what I think should happen here, but I want to see 
what the Forum thinks.  I will not bother the group with what the design team 
is suggesting I do.



Micah Davis

Ferguson Fire Design

micah.da...@ferguson.com<mailto:micah.da...@ferguson.com>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>