I am working on a project in a wood frame building where they have ceilings 
at varying heights. In the high ceiling areas (about 50% of the space), there 
is 5” between the ceiling and the bottom of the joists. These do not require 
sprinklers per 9.1.2.5. In the low ceiling areas, there is 10” to 12”, so 
concealed space sprinklers would need to be installed above those. There are 
also soffits along some walls that are 18” to 24” wide that technically would 
require sprinklers even though the surrounding areas don’t. Is there a point 
where I don’t need consider small spaces in placing CC’s?
  
  
  