If you’re not fluent in Spanish or a translation app uses, César’s message 
says, “According to the (NFPA 20) handbook, the 10x diameter provision doesn’t 
apply to vertical in-line electric pumps.”

Steve

From: César Gonzales <cgonza...@cosapi.com.pe>
Sent: Monday, October 09, 2023 7:15 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: Distance to fire pump suction

Estimados,
De acuerdo con HandBook, las 10 veces el diámetro no aplica si se trata de 
electrobombas vertical en línea.
Saludos.
CAGS.

De: John Denhardt 
<jdenha...@firesprinkler.org<mailto:jdenha...@firesprinkler.org>>
Enviado el: sábado, 7 de octubre de 2023 10:27
Para: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Asunto: [Sprinklerforum] Re: Distance to fire pump suction

NFPA 20 - 2023 edition is below.

Hmm. I see the issue. This will be added to AFSA NFPA 20 - 2028 list to clarify 
or address.


4.29.3 Devices in Suction Piping.

Where located in the suction pipe of the pump, check valves and backflow 
prevention devices or assemblies shall be located a minimum of 10 pipe 
diameters from the pump suction flange.





John August Denhardt, P.E.
Vice-President Engineering and Technical Services
American Fire Sprinkler Association
301-343-1457

On Oct 7, 2023, at 11:19, John Denhardt 
<jdenha...@firesprinkler.org<mailto:jdenha...@firesprinkler.org>> wrote:

I have always used the suction flange size of the fire pump.  The suction pipe 
size and backflow preventer size can vary.  I will look at NFPA 20 when I have 
a chance and see if I can find a reference for you.

Thanks,
John

[https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1]
John August Denhardt, PE
Vice President, Engineering and Technical Services
American Fire Sprinkler Association
m: p:
301-343-1457
214-349-5965 ext 121
w:
firesprinkler.org<http://firesprinkler.org/>


Sprinkler Hydraulic Calculations Workshop

AFSA’s three-day, in-person workshop provides a deep dive into the principles 
of hydraulics, including the different types of pressure, calculating changes 
in pressure (elevation and friction loss), and node analysis. Click 
here<https://www.firesprinkler.org/programs/calculations/> for details and to 
register.


On Sat, Oct 7, 2023 at 10:52 AM Fpdcdesign 
<fpdcdes...@gmail.com<mailto:fpdcdes...@gmail.com>> wrote:
Fire pump is a 250 gpm at 60 psi

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)


On Oct 7, 2023 at 10:48 AM, <Tstone52<mailto:tston...@comcast.net>> wrote:
Todd,

According to NFPA 20, 2013 ed., 4.26, Table 4.26 shows 4” minimum suction.

2022 ED. Is the same.

Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

   117 Old Stage Rd. - Essex Jct., VT. 05452
                 CELL: (802) 373-0638
             tston...@comcast.net<mailto:tston...@comcast.net>

From: Fpdcdesign <fpdcdes...@gmail.com<mailto:fpdcdes...@gmail.com>>
Sent: Saturday, October 7, 2023 10:16 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Distance to fire pump suction

I have a system with a 6” backflow preventer, which reduces to 4” immediately 
after. There is approximately 48” of 4” pipe to the suction flange on a 4 x 3 
pump. All elbows are turning correctly. Is this sufficient? Does the 10x rule 
apply to the size of the backflow preventer or the fitting directly attaching 
to the pump?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)
_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>
__________________________________________________________________________________
Aviso de Confidencialidad:
Toda la informacion contenida en este mensaje es confidencial y de uso exclusivo
de COSAPI S.A. su divulgacion, copia, adulteracion o cualquier otro tipo de 
accion
estan prohibidas y solo debe ser conocida por la persona a quien se dirige este
mensaje.
Si Ud. ha recibido este mensaje por error por favor proceda a eliminarlo y 
notificar
al remitente.
(Tildes omitidas intencionalmente)
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to