I would agree, I believe the only exception that would work in this case is the 
filled with non-combustible insulation one as the only other one that allows 
bar joist or other non-solid construction is a max 6” deep space.  We run into 
these non-solid members more and more often.  Makes me think I should see if 
the FPRF is doing anything with something like that and/or suggest it perhaps?

Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email mmo...@shambaugh.com<mailto:mmo...@shambaugh.com>
[cid:image001.png@01DA4881.8DBDFAF0]

From: Kevin Hall <kh...@firesprinkler.org>
Sent: Tuesday, January 16, 2024 1:20 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: Concealed Spaces Not Requiring Sprinkler 
Protection

I think it is still combustible within the concealed space as the top and 
bottom chords are solid wood members. . . might still be able to omit 
sprinklers if one of the scenarios in the installation chapter applies. Kevin 
Hall, M. Eng. , P. E. ,
ZjQcmQRYFpfptBannerStart
This Message Is From an External Sender
This message originated outside your organization.
ZjQcmQRYFpfptBannerEnd
I think it is still combustible within the concealed space as the top and 
bottom chords are solid wood members... might still be able to omit sprinklers 
if one of the scenarios in the installation chapter applies.

[https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1]
Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE
Sr. Manager, Engineering and Technical Services
American Fire Sprinkler Association
p:
214-349-5971
w:
firesprinkler.org<https://urldefense.com/v3/__http:/firesprinkler.org/__;!!FaxH778!YqTOqSha7Zzm_QYgyTvKAPixQl5uUFEJ9RXD7x9uSUpb8qCKKT8DTxs7v8NKgFv60CcQp_VLF8Ela3vRkJY$>

Treat Your Apprentices Like VIPs!
AFSA’s Virtual Instruction Program (VIP) for Apprentices is training that comes 
straight from our expert instructors. They lead the way to ensure your men and 
women are trained, letting you focus on OJT. Click 
here<https://urldefense.com/v3/__https:/www.firesprinkler.org/sprinkler-apprentice-training/__;!!FaxH778!YqTOqSha7Zzm_QYgyTvKAPixQl5uUFEJ9RXD7x9uSUpb8qCKKT8DTxs7v8NKgFv60CcQp_VLF8EljXCnfso$>
 to learn more and enroll.


On Tue, Jan 16, 2024 at 1:15 PM Steve Leyton 
<st...@protectiondesign.com<mailto:st...@protectiondesign.com>> wrote:
I believe that two layers of the Type X make the space between the presumably 
non-combustible ceiling and the sheetrock a non-combustible concealed space.


Steve Leyton

(Sent from my smartphone; please excuse typos and voice-to-text corruptions.)



-------- Original message --------
From: "George Medina Jr." 
<los_amigos_b...@yahoo.com<mailto:los_amigos_b...@yahoo.com>>
Date: 1/16/24 10:12 AM (GMT-08:00)
To: Discussion List On Issues Relating To Automatic Fire Sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Concealed Spaces Not Requiring Sprinkler Protection

There is a one hour floor assembly which consist of 22" Red-S joist (Wood 
Chords with Tube Bars) with 2 layers of type x gypsum board on channels below 
joist. Could it be considered limited combustible construction inside the bar 
joist? Or am I just grasping for straws, and it needs sprinklers.

Thanks For any replies,

George Medina Jr.


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!FaxH778!YqTOqSha7Zzm_QYgyTvKAPixQl5uUFEJ9RXD7x9uSUpb8qCKKT8DTxs7v8NKgFv60CcQp_VLF8EloJFCnLg$>
To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.