Assuming it is just an EOR requirement, and the EOR says install them, then
they should be installed - (I am not addressing this from a
monetary standpoint). However, the EOR has to clarify HOW to install them
specifically as it is outside the scope of the adopted standards/codes.
What size hose valve, flow and pressure requirements, Manual, Automatic,
Wet, Dry, etc. Where does the actual design criteria for the hose valve
come from?

Give them a price for a fire pump and interconnected standpipes and see how
that sits with them.



On Tue, Jan 23, 2024 at 8:13 AM Fpdcdesign <[email protected]> wrote:

> It is worth noting that the EOR (assumed in this case to be the specifying
> engineer) can request things that are beyond what the Code requires. Codes
> are a minimum, not an absolute.
>
> That being said, you should be able to get the “permit review comments”.
> Not sure who did them but it would seem that the AHJ would be doing them
> considering they issue the permits. Sounds more like the engineer’s review
> rephrased to make it sounds more mandatory.
>
> I would push back to the GC and tell him you can’t complete your work
> without a copy of those comments. Put the onus on them.
>
>
>
> On Jan 23, 2024 at 9:01 AM, <Travis Mack <[email protected]>> wrote:
>
> What is the height of the top floor?  What is the occupancy
> classification?  Go through 905 in the fire code and see what it says about
> standpipes.  From similar projects I have done over the years, I have not
> seen them required.  But, your local fire code will dictate.
>
>
>
>
>
> Travis Mack, SET
>
> *M.E.P.CAD* | Instructor / Support
>
> 181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
>
> www.mepcad.com | *m: 480.547.9348*|* Whatspp: +14805479348*
>
> *Email: [email protected] <[email protected]>*
>
>
>
> *AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD*
>
>
>
> *From:* James Litvak <[email protected]>
> *Sent:* Tuesday, January 23, 2024 6:55 AM
> *To:* AFSA Sprinkler Forum <[email protected]>
> *Subject:* [Sprinklerforum] Hose Valves in Townhome Apartments
>
>
>
> I am designing an NFPA 13 mid-rise apartment building that includes
> three townhome-style two-floor apartments. The EOR put a note on the FP
> plans to locate a hose valve on each floor of those units "AS REQUIRED." I
> didn't put them on my plans because I have never seen them required in
> similar units in other buildings. The EOR's review comments came back
> saying "Fire Protection permit review indicated hose valves required in
> 2-story units." I have requested the fire protection permit review comments
> and was told by the GC it is unlikely we'll receive them, and that I should
> just include those valves. My plans were approved by the AHJ without those
> valves. It is the EOR now refusing to accept my plans without the valves.
>
>
>
> Are those valves required?
> _________________________________________________________ SprinklerForum
> mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]



-- 

Greg McGahan

*Genesis Fire Services, LLC*

*4912 Glover Lane. Milton, FL **32570*

*P- 850-637-8535*

*C- 850-712-9555*
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to