Rachid,

There is no checklist for a maintenance procedure, but you could make your
own by following articles related to the monthly, semiannual and annual
inspection and maintenance listed in Chapter 11 of NFPA 2001 (2022 edition).

Most are visual inspections, containers in continuous service without the
need to refill or repair shall have a visual inspection every 5 years,
hoses shall be tested or replaced every 5 years. In my appreciation, the
one that requires most attention is the enclosure integrity. Sometimes
there are new perforations, penetrations, or even added volumes that can
affect the overall reliability of the system.

Hope this can be helpful for you.

Best!


On Mon, Mar 11, 2024 at 8:42 AM RACHID SAADAOUI <sa.rachid1...@gmail.com>
wrote:

> Hello everyone,
> I am working on the maintenance of a set of NOVEC1230 gas-based automatic
> detection and extinguishing systems, and I need a system maintenance
> checklist in accordance with NFPA2001
>
> Thanks,
> RACHID SAADAOUI
> Head of technical department
> OLP MORROCO
> 00212665648687
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkler.org



-- 
=?Este mensaje se dirige exclusivamente a su destinatario y puede contener
información privilegiada o confidencial. Si no es Ud. el destinatario
indicado, queda notificado de que la utilización, divulgación y/o copia sin
autorización está prohibida en virtud de la legislación vigente. Si ha
recibido este mensaje por error, le rogamos que nos lo comunique
inmediatamente por esta misma vía y proceda a su destrucción.


This message is intended exclusively for its addressee and may contain
information that is confidential and protected by professional privilege.
If you are not the intended recipient you are hereby notified that any
dissemination, copy or disclosure of this communication is strictly
prohibited by law. If this message has been received in error, please
notify us immediately via e-mail and delete it.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to