What is the total square footage of the building? If it is under 52,000 sq. ft. per 13 2016 8.2.4.3 they are not required.
Thanks, Gregg Fontes Lead Estimator O: 209-334-9119 gr...@cen-calfire.com<mailto:gr...@cen-calfire.com> [image001.jpg] This and any attached documents are for the use of the intended recipient(s) only and may contain information that is privileged, confidential, or work product that may be exempt from disclosure under applicable law. If you are not the intended recipient, any use, dissemination, distribution, or copying of this communication and any attachments is strictly prohibited, and you are hereby requested to delete this message and any attached documents, to destroy any printed copies, and to telephone or otherwise contact the sender immediately about the error From: chris.jo...@ci.urbana.oh.us <chris.jo...@ci.urbana.oh.us> Sent: Tuesday, April 09, 2024 4:57 AM To: sprinklerforum@lists.firesprinkler.org Subject: [Sprinklerforum] Floor Control Valves I have a 3 story older building being renovated with sprinkler system being added. My question is can AHJ require a floor control valve to be added to each floor. Plans only show 1 floor control valve for the first floor. 1st floor being business, 2nd and 3rd floor being residential and attic space being sprinklered also. Concern of freeze and break in attic on older building and to be able to isolate a floor after a fire. Thanks Chris Jones, Fire Marshal Urbana Fire Division