To endorse, in the West we won’t confirm the sun has come up before coffee. 
Without coffee it’s not important if the sun is risen.
 
Best.
 
Bruce.

> On 07/03/2024 8:35 AM PDT Steve Leyton <[email protected]> wrote:
>  
>  
> 
> Damn you guys – I’m not on vacation and was awake when Rick pinged as well.   
> This may come as a shock but we need our morning coffee and time to make 
> breakfast and #2 on the West Coast same as y’all. 
> 
>  
> 
> As they say, if you’re using an older edition of a standard  want to confirm 
> or clarify the committee’s intent on a particular issue, look at the most 
> current edition of that standard.   Moving from 2013 to 2016, there was a 
> subtle change in 7.5.3 where it was revised to say, “Where wet standpipes are 
> interconnected…”, so that clarifies the intent that it be applied to wet 
> only.  There’s also 7.5.4 that states, “Dry standpipes shall have only a 
> single level of interconnection”, so looping a dry manual was taken off the 
> table.
> 
>  
> 
> Jump ahead to 2024 and (renumbered) 9.4 has been simplified.   9.4.3 still 
> restricts dry standpipes to a single interconnection but overall, you can 
> interconnect at any level (unless the system is supplied by a rooftop tank), 
> no check valves are required, and with the AHJ’s approval standpipes don’t 
> need to be interconnected at all.  
> 
>  
> 
> When the committee opened discussion of the check valve requirement this past 
> cycle, we couldn’t figure out why that was even in the standard.   It’s been 
> there for so long that it became inertial at some point, I guess.   I/we have 
> gone over this quite a bit and, so long as there are sectional valves that 
> enable isolation of a standpipe, we couldn’t figure out why a check was 
> required.  
> 
>  
> 
> But I’m also concerned about looping manual standpipes because if there’s a 
> hydraulic advantage but the system has to be sectionally isolated, then a 
> dead-end calc’ should be the basis of design.   I’m a proponent of the KISS 
> theory.  (When Caputo and I were advocating and lobbying city building and 
> fire officials for residential fire sprinklers back in the 80’s he used to 
> say that the best and simplest residential sprinkler system was just pipe, 
> fittings and sprinklers and no extraneous valves or connections.    I agree 
> with that approach, especially with manual standpipes.)    There are 
> scenarios with multi-zone systems where interconnection to supply a higher 
> zone is one of the approved arrangements, but if I’m the AHJ, I’m down with a 
> single interconnection and no check valves, wet or dry.  
> 
>  
> 
> SL
> 
> Bright eyed and bushy tailed, whatever that’s supposed to mean
> 
>  
> 
>  
> 
>  
> 
> From: Jamie Seidl <[email protected]>
> Sent: Wednesday, July 03, 2024 5:44 AM
> To: [email protected]
> Subject: [Sprinklerforum] FW: 2013 NFPA 14 7.5.3
> 
>  
> 
> Quick question on a holiday week.
> 
> 7.5.3 states that "Where standpipes are interconnected at the top and bottom, 
> check valves shall be installed at the base of each standpipe to prevent 
> circulation”.
> 
> Is this requirement intended to apply to manual dry standpipes?  NFPA 14 does 
> not appear to make a distinction in this case, but if they're intended to 
> prevent circulation, I would imagine that is not a concern with a manual dry 
> system.
> 
> Steve, are you on vacation yet?  This one is up your alley.
> 
>  
> 
> Thanks for your time.
> 
>  
> 
> Jamie Seidl NICET SET #107472
> 
> Century Fire Protection http://www.centuryfp.com/ | General Manager
> 3600 Woodpark Blvd. Suite G Charlotte, NC 28206
> 
> ___________________________________________________________________
> 
> p  704 888 3473 tel:7048883473 |  m  704 650 0033 tel:7046500033 Facebook 
> https://www.facebook.com/CenturyFP   LinkedIn 
> https://www.linkedin.com/company/century-fire-protection   Twitter 
> https://twitter.com/centuryfp
> 
>  
> 
> 
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to [email protected]
> 
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to