Again, the spotlight shines on "Sprinkler Stockholm Syndrome".    

There's a fine line between high-level professional service and taking 
responsibility for the owner's tight grip on the budget.   "We know that the 
problem lies in the capacity of the fire pump, and the client wants to save as 
much as possible and reduce the risk due to the structural load."   So if the 
pump is the problem, why bang your head against the wall when there are serious 
potential downstream consequences to anchoring large diameter piping to 
existing framing?  Are you in a seismic zone?  If you're near DF, then the 
applied loads from sway bracing will be equal to or greater than the dead loads 
from hangers - do you know if the roof will even hold the weight of this 
two-riser configuration you're asking about?

Are you getting paid for multiple iterations of the design and will you liable 
to revise it if it gets shot down by a structural engineer or the owner's 
insurance?   If I was in your position (and I have been multiple times), my 
best advice to the owner would be to upsize the fire pump and be done with it.  
Work backwards from the maximum pipe sizing you're sure you can hang and brace; 
bring a structural engineer on board right now and have all aspects of the roof 
framing calc'd for the proposed loads of a spec' system design.  If the largest 
piping doesn't work, revise for a larger theoretical pump and re-calc' until 
the roof can bear both dead and live loads.  Then upsize the pump (as needed) 
to meet what is likely to be a higher pressure demand. 

Our firm currently has two ESFR upgrade projects at existing buildings here in 
Southern California and we are the design team lead.   One is three systems and 
one is nine; both buildings are 1980's vintage, one with wood truss framing and 
the other with panelized glu-lams and 4x purlins.  We have an architect, 
structural engineer and electrical engineer as subs and all aspects of the 
projects will be signed off by licensed professionals before they go out to 
bid.  Instead of taking ownership of what might be a festering pile of 
controversy, put it back on the owner to bring in ALL of the resources that 
THEY need to save THEMSELVES the money they don't want to spend on a new pump.  
 

Has there been a cost analysis of what upsizing the pump will cost?   Do you 
have electrical capacity to drive a bigger motor or is it a diesel?   How much 
will new underground service entries cost compared to a pump upgrade?   I'm 
having a hard time getting my head around how shortsighted this owner is. 

My Friday rant, DONE.

Felicidades, 
Esteban


Steve Leyton, President 
T  |  619.255.8964 x 102  |  www.protectiondesign.com 
2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108
Fire Protection System Design | Consulting | Planning | Training



-----Original Message-----
From: Gerzayn Fuentes @ KOLTEK.MX [mailto:[email protected]] 
Sent: Friday, July 19, 2024 12:59 PM
To: [email protected]
Cc: Francisco Reveles @ Koltek.mx <[email protected]>
Subject: [Sprinklerforum] UUP / Plastics A unexpanded exposed

Hello everyone!

We are designing an expansion project for an Plastic A Unexpanded Exposed or 
UUP with racks warehouse. Design specification is 12K25.2 @
60 psi + 250 gpm x 60 minutes. The existing pump is 2,000 gpm @ 120 psi, and an 
existing underground schedule 40 steel network is more than 10 years old. We 
are using a factor C=100.

The above gives us 4" branch lines, 8" mains and a 10" riser, using 3 mains and 
it gives us the curve, but we need to lower the pipe diameters. We have never 
seen a 10" riser. We know that the problem lies in the capacity of the fire 
pump, and the client wants to save as much as possible and reduce the risk due 
to the structural load.

Our question is, can we have a grid sprinkler system with 2 risers of 8" that 
feed it? We can't find anything in NFPA or FM Global standards that prevents 
this, but at the same time I've never seen a system like this installed.

Greetings and we look forward to comments.
-- 

Gerzayn Fuentes Campos / director general [email protected] México.
www.koltek.mx

--
 <https://expofire.ownersys.com/registro>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to