Not coming out of, but sharing the water supply with the building.   
Simplistically, if your building standpipe system is manual, then you can place 
your FDC on the service lateral and then split to separate building and dock 
systems.   Again, maybe the local AHJ will buy it coming off the building 
system, but if it’s pumped for whatever reason, I’m a hard no on the 1,000 gpm 
water supply.   Boat fires are different and so are response strategies, 
including joint response with a fire boat.   If they think they may need 1,000, 
my first pass would be manual/manual and design the water supply so they can 
pump it.

This and the preceding emails on this thread represent my personal opinion only 
and are not intended to represent NFPA or the NFPA 14 technical committee.

Steve L.



From: John Irwin <[email protected]>
Sent: Tuesday, July 30, 2024 1:18 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Dock System / Stand pipe

Ok understood. I mean that’s an argument for me doing what I want to do with 
the stand pipe system.

John Irwin
Florida Fire Sprinkler Division
Solomon Plumbing

From: Steve Leyton 
<[email protected]<mailto:[email protected]>>
Sent: Tuesday, July 30, 2024 4:16 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Dock System / Stand pipe

2023 Florida Building Code, 8th Edition:

[F] 905.8 Dry standpipes.
Dry standpipes shall not be installed.
Exception: Where subject to freezing and in accordance with NFPA 14.


From: John Irwin <[email protected]<mailto:[email protected]>>
Sent: Tuesday, July 30, 2024 1:10 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Dock System / Stand pipe

Probably not doing that.  =)  Florida Building Code and Florida Fire Prevention 
Code are as far as I dig.



John Irwin
Florida Fire Sprinkler Division
Solomon Plumbing

From: Steve Leyton 
<[email protected]<mailto:[email protected]>>
Sent: Tuesday, July 30, 2024 4:08 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Dock System / Stand pipe

Evuhbody needa reeda IBC §905.8.

From: Fpdcdesign <[email protected]<mailto:[email protected]>>
Sent: Tuesday, July 30, 2024 1:01 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Dock System / Stand pipe

Far am I to challenge Mr Layton on a standpipe question. However, my first 
reaction was why not. Pumps and underground are shared between buildings, why 
not between a building and a marina? Connected to a 1000 gpm pump, it would 
most likely end up automatic wet instead of manual dry.

This opinion is based only on information previously received. There may be 
other circumstances that could make the preferred outcome different.

Todd Williams
Fire Protection Design/Consulting
Stonington, CT
860-608-4559

On Jul 30, 2024 at 3:06 PM, <John Irwin<mailto:[email protected]>> 
wrote:
I have a situation I have not come across before. New construction of an 8 
story hotel at the marina. Plans also call for a manual dry dock hose system. 
This will require, one, maybe two hose valves. The dock is located on the side 
of the hotel opposite the street. Civil plans call for an underground run from 
the front of the hotel, all the way around the property, along the sea wall, to 
the dock.

I have a stair well, with a stand pipe in it, about 20 ft from where the dock 
hose valves would need to be.

Can I delete the manual dry hose and feed from the hotel stand pipe system? Or 
even directly from the fire pump would be preferable to all the underground 
work. Can I change the FDC sign on the front of the hotel to include the dock 
hose valves? “Hotel & Dock FDC”

My pump is already 1000GPM. Would adding these hose valves effectively make 
them part of the stand pipe system? Is there any reason in NFPA 13 or 14 that I 
can’t extend my stand pipe system out horizontally?

John Irwin
Florida Fire Sprinkler Division
Solomon Plumbing
www.solomonplumbing.net
Cell: 727-282-9243
Office: 248-486-1600 (Corporate)

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.” – Benjamin Franklin

_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to