AJ, NFPA 13D, 2025 EditionA.6.5.2
The 5 gpm (20 L/min) provision is intended to be per connection and not per dwelling unit. A townhouse with more than two dwelling units fed by a common water connection would only require 5 gpm (20 L/min) to be added to size the common piping. Does this answer your question? Tom Wellen [email protected] On Wed, Aug 7, 2024 at 1:39 PM Anthony Johnson <[email protected]> wrote: > Good afternoon, > A quicky: 13D requires 5 gpm when there is "more than one dwelling unit". > I have about eight being a townhome - each getting their own system but a > common feed and only one meter. Should I include 5 gpm for ea unit or just > 5 gpm for the whole lot? > > Thanks, > AJ > > > _________________________________________________________ > SprinklerForum mailing list: > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org > To unsubscribe send an email to > [email protected]