NFPA 13D, 2025 EditionA.6.5.2

The 5 gpm (20 L/min) provision is intended to be per connection and not per
dwelling unit. A townhouse with more than two dwelling units fed by a
common water connection would only require 5 gpm (20 L/min) to be added to
size the common piping.


Does this answer your question?



Tom Wellen

[email protected]




On Wed, Aug 7, 2024 at 1:39 PM Anthony Johnson <[email protected]>
wrote:

> Good afternoon,
> A quicky: 13D requires 5 gpm when there is  "more than one dwelling unit".
> I have about eight being a townhome - each getting their own system but a
> common feed and only one meter. Should I include 5 gpm for ea unit or just
> 5 gpm for the whole lot?
>