If located where ICC Fire Code is applicable, then mattresses are within the 
definition of ICC high piled storage, if six feet or higher.  Then in ICC 
Chapter 32, section 3203.6 mattresses are further defined/included as 
"high-hazard commodities", presenting special fire hazards beyond those of 
class I, II, III or IV.....".  Architect may be needed to coordinate the many 
aspects, beyond sprinkler protection, within the high-piled chapter.


On Aug 8, 2024 8:31 PM, Fpdcdesign <[email protected]> wrote:
You don't often get email from [email protected]. Learn why this is 
important<https://aka.ms/LearnAboutSenderIdentification>
What Steve said. I did a large project with a foam mattress manufacturer a 
while back. We pretty much dismissed the flammability standards argument right 
away. it may slow it down a little but it’s still a foamed plastic.

Todd Williams
Fire Protection Design/Consulting
Stonington, CT
860-608-4559


On Aug 8, 2024 at 8:13 PM, <Steve Leyton<mailto:[email protected]>> 
wrote:

Seriously?

Foam mattresses are required to have a nonflammable barrier, but that's just a 
rating on the material used to cover and bind it. In most states mattress 
toppers aren't required to be  certified. Polyfoam is polyfoam and it's a wee 
bit flammable.

CEP


Steve Leyton

Sent from my "Smart" Phone, so apologies for any typos or voice-to-text 
corruptions.



-------- Original message --------
From: "Kyle.Montgomery" <[email protected]>
Date: 8/8/24 3:34 PM (GMT-08:00)
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Mattress Storage Classification

I’m working with a client who wants to store mattresses in racks. They are foam 
mattresses, so these would be group A expanded plastics (EP). Each of the 
mattresses is rolled up and packaged in a cardboard box. So, cartoned expanded 
plastics (CEP), right?

The customer (who is very knowledgeable about the mattress manufacturing 
process and requirements) wants to argue that mattresses should not just 
automatically fall into the “High-hazard (Group A Expanded)” category because 
of the strict flammability standards that mattresses are legally required to 
meet, specifically CFR 1633 – Standard for the Flammability (Open Flame) of 
Mattress Sets.

What are your thoughts on this? I have my own ideas, but I was wondering if 
anyone had gone down the path before. Do you think the client’s assertion has 
merit? Why or why not?

Thanks.

Kyle Montgomery
Aero Automatic Sprinkler Co.
[email protected]<mailto:[email protected]>

_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to [email protected]
CAUTION: This email originated from outside of our organization. Do not click 
links or open attachments unless you recognize the sender and know the content 
is safe.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to