The 22 year history in NFPA 13 and the excellent rationale presented in the 
SFPE Position Statement (4.2 Tasks) may never address this (in my opinion).  
I’ve been monitoring this list since 1996 and have seen numerous drawing notes 
to “sprinkle per NFPA 13”. We routinely bemoan the plight of sprinkler 
contractors who are expected to be process engineers, structural and seismic 
specialists, and building code experts. The Endorsing Organizations need to 
convene and create a set of IBC/IFC proposals to put this into the hands of the 
Building and Fire Officials to address two key points 1) contents 
identification by Owner and 2) hazard classification by EOR. As a start I’d 
suggest modifications to IBC Sections 105 and 107 to do this. Maybe start by 
adding “fire protection systems” to IBC 105.1?

Bill Brooks

William N. Brooks P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410 544 3620 o
412-400-6528 c

From: John Denhardt <[email protected]>
Sent: Monday, October 28, 2024 1:00 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Metal manufacturing

Without.  Sorry.  Coming off a long weekend.

Always obtain an owner's certificate.

Thanks,
John

[https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1]
John August Denhardt, PE
Vice President, Engineering and Technical Services
American Fire Sprinkler Association
m: p:
301-343-1457
214-349-5965 ext 121
w:
firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__firesprinkler.org&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=iih4NVEkD89x14qk7m6LbFsl49j-eQ0kuCE55fl2VOI&m=yHL2YFVnEz0E0zcF2jLJxpYX4DvW9Zt8QYcNyeUH_wh73Xpg1mguTqAeoQr7K0in&s=QC7AFCZA6wsmY-ZrItWd39zLputSQSjNxyLTQqTjItc&e=>


Enroll Now for Level 2 VIP Classes

AFSA’s Virtual Instruction Program (VIP) for apprentices is live classroom 
training that comes straight from our expert instructors. They lead the way to 
ensure your men and women are trained, letting you focus on OJT. A new Level 2 
class begins Oct. 8, 2024. Click 
here<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.firesprinkler.org_sprinkler-2Dfitter-2Dapprentice-2Dtraining-2Dvip_&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=iih4NVEkD89x14qk7m6LbFsl49j-eQ0kuCE55fl2VOI&m=yHL2YFVnEz0E0zcF2jLJxpYX4DvW9Zt8QYcNyeUH_wh73Xpg1mguTqAeoQr7K0in&s=EtTOwhAfDPfUivi7Y8zgglBM3mCYRL3XluoPIW-SjF4&e=>
 to learn more and enroll!




On Mon, Oct 28, 2024 at 12:58 PM Spectrum 
<[email protected]<mailto:[email protected]>> wrote:

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=https-3A__lists.firesprinkler.org_list_sprinklerforum.lists.firesprinkler.org&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=iih4NVEkD89x14qk7m6LbFsl49j-eQ0kuCE55fl2VOI&m=yHL2YFVnEz0E0zcF2jLJxpYX4DvW9Zt8QYcNyeUH_wh73Xpg1mguTqAeoQr7K0in&s=QXI7GQaHN1siQnEOSBpVIyYbbmiIIhah3Y4dFhF7lSc&e=>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
“A contractor or an AHJ moving forward with a properly signed certificate is 
asking for increased liability.”

Did you mean “with” OR “without” ?

Timothy Goins
RME & SCR holder

________________________________
From: John Denhardt 
<[email protected]<mailto:[email protected]>>
Sent: Monday, October 28, 2024 8:14 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Metal manufacturing

Matt - Please be careful in what you state.

NFPA 13 only references you stated are in the annex which are typical 
suggestions.  The annex list is not to be used without fully understanding the 
specific process and the actual descriptions in the body of the standard.  
Relying on the annex for your determination of a hazard could lead to an issue.

I also want to state that I really like what I'm reading from other posts.  I 
have been beating the drum for over 5 years categorizing the hazard, water 
supply evaluations, and other items are engineering.  In the real world where 
lawyers are involved, a technician who does not have a professional engineers 
license is exposing themselves to liability.  The SFPE Position paper 2020-1 
which has been endorsed by many associations including AFAA, AFSA, ASCET, 
NICET, NFSA, NSPA, and others is very clear..  The "Design Basis - Owner 
Certificate" is the owner's or owner's agent responsibility.  Period!  NFPA 13 
requires this certificate to be submitted with the working plans.  A contractor 
or an AHJ moving forward with a properly signed certificate is asking for 
increased liability.

NFPA 13 -2025 - 28.1.1.1 - Working plans submittals shall include the 
following:  (4) - Signed owner's certificate

Heck - this requirement has been around for a bit.  The concept of the Owner's 
Certificate was included in the 2002 edition of NFPA 13.

As part of your proposal and contract for a project, insist on a properly 
filled and executed certificate.  The sample in the annex is a starting point.  
If you feel the need to add information, make a form and have the responsible 
party take the liability off you.

Feel free to contact me directly if you have any questions on this topic.  
AFSA's position is clear.and my technical team understands this position.

SFPE position's paper is available on the web by searching SFPE Position 
statement 2020-1, PS 2020-1 The Engineer and the Engineering Technician 
Designing Fire Protection Systems

The above is my opinion and has not been processed as a formal interpretation 
in accordance with the NFPA Regulations Governing Committee Projects. This is 
provided with the understanding that the AFSA assumes no liability for this 
opinion or actions taken on it and they are not to be considered the official 
position of the AFSA, and/or NFPA or its technical committees.AFSA cannot 
provide design or consulting engineering services, and this opinion should 
therefore not be considered, nor relied upon, as such.

Thanks,
John

[https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1]
John August Denhardt, PE
Vice President, Engineering and Technical Services
American Fire Sprinkler Association
m: p:
301-343-1457
214-349-5965 ext 121
w:
firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__firesprinkler.org_&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=iih4NVEkD89x14qk7m6LbFsl49j-eQ0kuCE55fl2VOI&m=yHL2YFVnEz0E0zcF2jLJxpYX4DvW9Zt8QYcNyeUH_wh73Xpg1mguTqAeoQr7K0in&s=YYJW2xP63IRdcKFfw8kK_wN1YBWTyyks6nBs_se3NlQ&e=>



Enroll Now for Level 2 VIP Classes

AFSA’s Virtual Instruction Program (VIP) for apprentices is live classroom 
training that comes straight from our expert instructors. They lead the way to 
ensure your men and women are trained, letting you focus on OJT. A new Level 2 
class begins Oct. 8, 2024. Click 
here<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.firesprinkler.org_sprinkler-2Dfitter-2Dapprentice-2Dtraining-2Dvip_&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=iih4NVEkD89x14qk7m6LbFsl49j-eQ0kuCE55fl2VOI&m=yHL2YFVnEz0E0zcF2jLJxpYX4DvW9Zt8QYcNyeUH_wh73Xpg1mguTqAeoQr7K0in&s=EtTOwhAfDPfUivi7Y8zgglBM3mCYRL3XluoPIW-SjF4&e=>
 to learn more and enroll!



On Thu, Oct 24, 2024 at 4:51 PM 
<[email protected]<mailto:[email protected]>> wrote:
I love all you guys. I really do. (Even you Todd)

But, Hire an Engineer, or Should be provided by an Engineer, just does not work 
out here in the trenches.

The answer is there in 13. Even "extruding" by a 3-D printer is extruding. I 
had to do Metal Working for folks cutting 4x8 sheets of aluminum.
There is not a distinction. Some AHJ's see that and live by it.

 IS it the intent? Probably not.

But it IS what the book says.

Which is the only thing we have in most cases.

I really wish we could kick it back. But more times than not, they just go to 
the next person in line.

Just saying. Those are not really answers to the questions.

Rant over..

R/
Matt



Matthew J. Willis, CWBSP, C.E.T.

Ferguson Fire Design, LLC

D: (602) 
337-0721<https://urldefense.proofpoint.com/v2/url?u=http-3A__-28602-29-2520337-2D0721&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=iih4NVEkD89x14qk7m6LbFsl49j-eQ0kuCE55fl2VOI&m=yHL2YFVnEz0E0zcF2jLJxpYX4DvW9Zt8QYcNyeUH_wh73Xpg1mguTqAeoQr7K0in&s=KGNZnrS7hcHXE2h9lSoDE7AO-C4hN6LjFjEQqF5pbzM&e=>
 C: (307) 
236-8249<https://urldefense.proofpoint.com/v2/url?u=http-3A__-28307-29-2520236-2D8249&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=iih4NVEkD89x14qk7m6LbFsl49j-eQ0kuCE55fl2VOI&m=yHL2YFVnEz0E0zcF2jLJxpYX4DvW9Zt8QYcNyeUH_wh73Xpg1mguTqAeoQr7K0in&s=C64l1h743-daQ6AanrHb-jLtEqYBQfVS0oHFnSMrpDQ&e=>

[email protected]<mailto:[email protected]>



________________________________
From: Craig Hanson <[email protected]<mailto:[email protected]>>
Sent: Thursday, October 24, 2024 12:48 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Metal manufacturing

Caution:  This email originated from outside of the organization.  DO NOT click 
links or open attachments unless you recognize and trust the sender.
________________________________
They need to provide for you the hazard analysis that should have been done by 
an FPE and in accordance with IFC 104.7.2 and NFPA 13: 4.2(2022). The AHJ 
should have requested that information also. These are tricky operations as 
dissimilar metals create a deflagration issue. the design may also be outside 
the scope of the NFPA 13 due to the process involved. Their insurance company 
should also be requiring a hazard analysis.



Craig D. Hanson, CFPS
Fire Division Manager
West Coast Code Consultants, Inc. (WC³)
Meridian Satellite Office
C: 253.225.9977 | E: [email protected]<mailto:[email protected]> | 
www.WC-3.com<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.wc-2D3.com_&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=iih4NVEkD89x14qk7m6LbFsl49j-eQ0kuCE55fl2VOI&m=yHL2YFVnEz0E0zcF2jLJxpYX4DvW9Zt8QYcNyeUH_wh73Xpg1mguTqAeoQr7K0in&s=uKgAVgFTGJarxQOoUnEjm1LUJOCwclM_e1whnT8slWk&e=>
Teaming With Your Community to Make a Difference


On Thu, Oct 24, 2024 at 12:21 PM Fpdcdesign 
<[email protected]<mailto:[email protected]>> wrote:
+1 for Tim Stone. Too often the contractor or their estimator are asked to 
figure out design criteria. That should fall upon the FPE.

Todd Williams
Fire Protection Design/Consulting
Stonington, CT
860-608-4559



On Oct 24, 2024 at 1:04 PM, <Tstone52<mailto:[email protected]>> wrote:

It should be recommended that an “Architect” or “Engineer of Record” should 
provide you with a Code Review.

Or hire a “Fire Protection Engineer” to assist you.



Regards,

G. Tim Stone



G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services



   117 Old Stage Rd. - Essex Jct., VT. 05452

                 CELL: (802) 373-0638

             [email protected]<mailto:[email protected]>



From: Bobby Welch <[email protected]<mailto:[email protected]>>
Sent: Thursday, October 24, 2024 12:57 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Metal manufacturing



I have a building were they are making metal products by multiple processes 
including Metal Casting of steel, Metal Forging, Additive Manufacturing and hot 
rolling. Most of the building is open warehouse where they are producing metal 
products with 3D printers.  NFPA has metal workings listed as ordinary hazard 
but also has Die Casting and Metal extruding under Extra hazard group 1. Does 
anyone know where I would start to figure out what hazard is required for this 
building?

Bobby Welch | Sprinkler Systems Designer
KOORSEN FIRE & SECURITY
8090 N Dixie Dr, Dayton, OH 45414
P 937.641.8403 | Ext. 0318 | M 937.594.8457
[email protected]<mailto:[email protected]> | 
www.koorsen.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.koorsen.com&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=iih4NVEkD89x14qk7m6LbFsl49j-eQ0kuCE55fl2VOI&m=yHL2YFVnEz0E0zcF2jLJxpYX4DvW9Zt8QYcNyeUH_wh73Xpg1mguTqAeoQr7K0in&s=MTrNRzpjIpOUHwGyo53sBwSCKr-Nm8HLBNGmHkP_-6M&e=>

24x7x365 Service: 937.660.7050 | 
[email protected]<mailto:[email protected]>
_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=https-3A__lists.firesprinkler.org_list_sprinklerforum.lists.firesprinkler.org&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=iih4NVEkD89x14qk7m6LbFsl49j-eQ0kuCE55fl2VOI&m=yHL2YFVnEz0E0zcF2jLJxpYX4DvW9Zt8QYcNyeUH_wh73Xpg1mguTqAeoQr7K0in&s=QXI7GQaHN1siQnEOSBpVIyYbbmiIIhah3Y4dFhF7lSc&e=>
 To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=https-3A__lists.firesprinkler.org_list_sprinklerforum.lists.firesprinkler.org&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=iih4NVEkD89x14qk7m6LbFsl49j-eQ0kuCE55fl2VOI&m=yHL2YFVnEz0E0zcF2jLJxpYX4DvW9Zt8QYcNyeUH_wh73Xpg1mguTqAeoQr7K0in&s=QXI7GQaHN1siQnEOSBpVIyYbbmiIIhah3Y4dFhF7lSc&e=>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=https-3A__lists.firesprinkler.org_list_sprinklerforum.lists.firesprinkler.org&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=iih4NVEkD89x14qk7m6LbFsl49j-eQ0kuCE55fl2VOI&m=yHL2YFVnEz0E0zcF2jLJxpYX4DvW9Zt8QYcNyeUH_wh73Xpg1mguTqAeoQr7K0in&s=QXI7GQaHN1siQnEOSBpVIyYbbmiIIhah3Y4dFhF7lSc&e=>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

And I will give them one heart, and I will put a new spirit within you; and I 
will take the stony heart out of their flesh, and will give them an heart of 
flesh…
Eze 11:19
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to