If you can size it without the fire pump, then just tee off after the backflow 
preventer and before the fire pump.  Make sure you meet all requirements for 
the right angle flow with the tee, if it needs to be considered, per NFPA 20 
and you should be good to go.  The pump shall be sized for the greatest demand 
downstream of the pump.  If you place the L1 system upstream of the fire pump 
then the pump doesn't need to provide for it.





Travis Mack, SET

M.E.P.CAD | Instructor / Support

181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348| Whatspp: +14805479348

Email: [email protected]<mailto:[email protected]>



AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD



Academy of Fire Sprinkler Technology | Director, Engineering Technology

101 S Main Street, Suite 001, Decatur, IL 62523

________________________________
From: Jeff Brickell <[email protected]<mailto:[email protected]>>
Sent: Tuesday, November 19, 2024 8:06 AM
To: 
[email protected]<mailto:[email protected]>
 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Fire Pump Sizing


I have a situation that's unique to me and am looking for some guidance.



I have a 7-story building.  The first level contains a parking garage with a 
demand of 635 GPM @ 61 PSI.  The municipal supply can meet this demand.



The 7th floor has a remote area with a demand of 285 GPM @ 66 PSI, which the 
municipal supply cannot meet.



NFPA 20 says to size a fire pump to meet the greatest demand.  If I can meet 
the level 1 demand without a pump, why would I need to size a fire pump for it? 
 There would be a drastic size reduction if I only had to meet the 7th floor 
demand.



I have reached out to a couple other people, and they have all said I need to 
size the pump to the garage demand, I am just curious as to why.



If the contractor were to tee the underground and bring up a second supply for 
the first floor only would that be acceptable to then not use a pump?  Maybe 
there is something I'm not considering or thinking of since this is new to me.



Any advice, comments welcome, thank you.





Jeff Brickell, CET

Senior Estimator/Designer

NICET III CERTIFIED

CERT #147245



OREGON CERTIFIED COBID FIRM #13272

(EMERGING SMALL BUSINESS)



TRIAD FIRE PROTECTION

[cid:[email protected]]

OREGON . WASHINGTON . ARIZONA



OFFICE  503.856.6333

CELL       602.550.4292

FAX        866.766.8862


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to