I say OS&Y gate valve only required on pump suction unless 50 feet away can use 
butterfly valve. Or something like that. Can't imagine where that would happen 
50 ft.

All other valves shown in diagram can be butterfly valves. I always put 
butterfly on each side of bypass check for servicing.

That the way I see it.


Jeff Normand
Engineering Designer III
Ferguson Fire Design, LLC

Ferguson Fire & Fabrication
D: 602-337-0725
jeff.norm...@ferguson.com<mailto:jeff.norm...@ferguson.com>

ferguson.com<http://www.ferguson.com/>

From: Hinson, Ryan <rhin...@burnsmcd.com>
Sent: Tuesday, February 4, 2025 3:29 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Enforceable as though Standard versus Annex language

Caution:  This email originated from outside of the organization.  DO NOT click 
links or open attachments unless you recognize and trust the sender.
________________________________
Ran into a scenario where there is disagreement on whether Annex A information 
is enforceable since the Standard language specifically calls out an Annex 
figure:
Here is the language from NFPA 20 (2022) Section 4.16.4 regarding bypass 
configurations and whether gates both up- and downstream of the bypass check 
are required:
[cid:image002.png@01DB771A.B27CF3F0]
Here is the explicitly referenced Annex figure:
[cid:image003.png@01DB771A.B27CF3F0]
I assert that, if explicitly referenced (as if referencing an outside 
document), that document becomes part of the standard and is enforceable as 
such.  There are those who disagree and says that unless the Annex is formally 
adopted, it is not required.

What say you?

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Associate Fire Protection Engineer \ Upper Midwest Region
O 612-900-3755 \  M 763-688-4045 \  F 952-229-2923
rhin...@burnsmcd.com<mailto:rhin...@burnsmcd.com>  \  
burnsmcd.com<http://www.burnsmcd.com/>
8201 Norman Center Drive, Suite 500  \  Bloomington, MN 55437
*Registered in: AK, LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to