Sorry Ken.

I was referring to the tank on the apparatus. They normally hold 1000.

I will be careful next time I hip shoot..

R/
Matt


Matthew J. Willis, C.E.T.

Ferguson Fire Design, LLC

D: (602) 337-0721<tel:6023370721> C: (307) 236-8249<tel:3072368249>

[email protected]<mailto:[email protected]>



________________________________
From: Parsley Consulting <[email protected]>
Sent: Wednesday, October 8, 2025 1:22 PM
To: [email protected] 
<[email protected]>
Subject: [Sprinklerforum] Re: Fire station

Caution:  This email originated from outside of the organization.  DO NOT click 
links or open attachments unless you recognize and trust the sender.
________________________________
Matt,

I'm not sure I understand your remark on "1000 gpm of water present in the 
hazards."

color me baffled by this,
Ken Wagoner, SET
Parsley Consulting
3002 Younger Drive
Harrisonville, Missouri 64701-3909
Phone: (760) 745-6181
Visit the 
website<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>

On 10/8/2025 2:18 PM, 
[email protected]<mailto:[email protected]> wrote:
Having worked in these many years ago, I would find it a stretch to go to 
garage, or machine..

There is 1000gpm of water present in the hazards..

R/
Matt


Matthew J. Willis, C.E.T.

Ferguson Fire Design, LLC

D: (602) 337-0721<tel:6023370721> C: (307) 236-8249<tel:3072368249>

[email protected]<mailto:[email protected]>



________________________________
From: Parsley Consulting <[email protected]><mailto:[email protected]>
Sent: Wednesday, October 8, 2025 1:16 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]><mailto:[email protected]>
Subject: [Sprinklerforum] Fire station

Caution:  This email originated from outside of the organization.  DO NOT click 
links or open attachments unless you recognize and trust the sender.
________________________________
Having a bit of confusion.

A project is to follow the 2022 edition of NFPA 13.

The apparatus bays of a fire station have been designated on the plan as 
ordinary hazard, group 1.  When I look at the examples in §A.4.3.3.2, it seems 
to me that those spaces would be similar to (2) "automobile parking garages", 
or (14) "machine shops", or (24) "repair garages."  This would make the space 
similar to ordinary hazard group 2, which increases the required density from 
0.15 gpm/ft² to 0.20 gpm/ft².

Am I looking this incorrectly?  Any help greatly appreciated.

sincerely,
--
Ken Wagoner, SET
Parsley Consulting
3002 Younger Drive
Harrisonville, Missouri 64701-3909
Phone: (760) 745-6181
Visit the 
website<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>




_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to