I've run into a situation where we have a sidewall sprinkler in a restroom (57 
ft2).  A small cabinet (for linens) was put up on the same wall about 4" below 
our head.
I am of the opinion that the cabinet creates an obstruction and either the 
sprinkler needs to move or the cabinet.

My field foreman makes a pretty strong argument that 6.4.6.3.2 allows the 
sprinkler to be installed without consideration to obstructions. Technically, a 
restroom is considered a compartment and as mentioned earlier, it is smaller 
than 400 ft2.
Do you believe NFPA's intent for paragraph 6.4.6.3.2 was to also include 
bathrooms? I would say no.