From Tom’s response:

Depending on start method, engines can stop themselves both on low oil and high temperature.  But, these actions will generate an alarm condition to the controller and hopefully alarm system.


I’m confused. NFPA 20 prohibits shutdown of a fire pump diesel driver in a fire condition except for an over speed condition. 

Thanks,

John


John August Denhardt, P.E

Vice President Engineering and Technical Services
American Fire Sprinkler Association
301-343-1457

Are you a member with a technical question? 

Don't forget one of the most valuable resources that AFSA provides is Technical Reviews by our Technical Services Department. It’s like having an FPE on your staff. Visit www.firesprinkler.org/technicalreview to submit a question today! (Member login required.)  


On Jan 6, 2026, at 10:47, THOMAS J DUROSS <[email protected]> wrote:

Depending on start method, engines can stop themselves both on low oil and high temperature.  But, these actions will generate an alarm condition to the controller and hopefully alarm system.
 
TD
On 01/06/2026 8:50 AM ES