I did contact a fire code official and in this township (Pennsylvania) they are 
enacting an ordinance that says to use the 25 edition of 13 and make it .4 over 
2000 ft for showrooms and service bays.  But I could not find it in the newest 
edition.
Jay Stough 
NICET IV LAYOUT 
NICET III ITM 

   ----- Forwarded Message ----- From: daren welborn <[email protected]>To: Jay 
Google <[email protected]>; Discussion list on issues relating to automatic 
fire sprinklers <[email protected]>Sent: Wednesday, 
January 14, 2026 at 09:53:05 AM ESTSubject: Re: [Sprinklerforum] EV Charging
 Ive been instructed by our AHJ to use .30 over the area where charging 
stations are located plus another 10'-0" away from them.  This was in florida 
and im not sure where you are located but a quick call to your AHJ always helps.
From: Jay Google <[email protected]>
Sent: Wednesday, January 14, 2026 9:18 AM
To: Sprinkler Forum <[email protected]>
Subject: [Sprinklerforum] EV Charging 
I heard that in NFPA 13 (2025) there is something about charging stations being 
designed to EH2, but cannot find it.  Anyone know where it is?
Jay StoughNICET IV LAYOUTNICET III ITM  
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to