To your last comment, I think it’s contextual but there are exceptions to just 
about everything.

This is in CA.   Our state requires every single dwelling unit to be 
sprinklered, included ADUs.   We also limit plumbing fixtures to delivering the 
minimum usable flow that can be produced by the fixture industry.  1.28 gal per 
flush for toilets, for ex.   Faucets and shower heads are like mister bottles, 
1.2-1.8 gpm.  The only unregulated fixture in a home would be a pot filler at 
the stove, and those can be up to 5 gpm, so that’s about the only fixture that 
could threaten to trip a switch; if we could set a switch at 10-12 gpm, it 
would reliably ring on sprinkler flow but not domestic, especially for passive 
purge because… 1.28 gal per flush.

SL

From: Brett Peters <[email protected]>
Sent: Friday, February 13, 2026 9:18 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Waterflow Switch for combined/passive purge 
systems

I would be interested to see if there is something available for this scenario 
but I have my doubts, I would think in the case where you have the municipality 
demanding flow alarms for the sprinkler system the sprinkler and domestic when 
then need to be separated and could no longer be a combined system. No matter 
what you have a flow switch set at, there are going to be moments where 
domestic demand could set it off.



Thanks

Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
[email protected]<mailto:[email protected]>
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at 
www.proudline.ca<https://url.avanan.click/v2/r01/___http:/www.proudline.ca/___.YXAzOnByb3RlY3Rpb25kZXNpZ25hbmRjb25zdWx0aW5nOmE6bzphZmM5MzM4OTAyYjJiNmZkNWFjMmI4MzNkOTVjMWNjZDo3OjBiZWU6YTRmYTFmNTgzZjNlYzIyODQyMjMyM2NhOTE5NmI4NTMyM2JkODU5YTQ2OWRiOGIxNTNjZDk2ZjFmY2QxMTJiYTpoOlQ6Rg>


On Fri, Feb 13, 2026 at 6:36 AM 
<[email protected]<mailto:[email protected]>> wrote:
Damn Steve, talk about a "Friday" question..

A quick search puts us outside of industry and around a grand.

This interests me, so I may peek around a bit further when I get a chance?

Listing issues? IAW 72 or jurisdiction etc.?

R/
Matt


Matthew J. Willis

Ferguson Fire Design, LLC

D: (602) 337-0721<tel:6023370721> C: (307) 236-8249<tel:3072368249>

[email protected]<mailto:[email protected]>


[cid:[email protected]]<https://url.avanan.click/v2/r01/___https:/outlook.office.com/bookwithme/user/[email protected]?anonymous&ep=signature___.YXAzOnByb3RlY3Rpb25kZXNpZ25hbmRjb25zdWx0aW5nOmE6bzphZmM5MzM4OTAyYjJiNmZkNWFjMmI4MzNkOTVjMWNjZDo3OjVmYjU6NWI3NDVjNWMxNGNjNzFlODFhMDg5MTI2MTE1NmVkNjU5M2M5OGZhZmZkMWNhZmE1NTRlMjQ3Y2Y2NzY3MTZkYjpoOlQ6Rg>
Book time to meet with 
me<https://url.avanan.click/v2/r01/___https:/outlook.office.com/bookwithme/user/[email protected]?anonymous&ep=signature___.YXAzOnByb3RlY3Rpb25kZXNpZ25hbmRjb25zdWx0aW5nOmE6bzphZmM5MzM4OTAyYjJiNmZkNWFjMmI4MzNkOTVjMWNjZDo3OjhjNTA6NTMyYTNhNGVhNjIzNDdjYTVjNGFjNWRmN2QxNjEyNzkyZDRhYWNmNTU5ZjlhMzZlYTJlY2QyZTAzNDhkOWVhZTpoOlQ6Rg>
________________________________
From: Steve Leyton 
<[email protected]<mailto:[email protected]>>
Sent: Thursday, February 12, 2026 4:43 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Waterflow Switch for combined/passive purge systems


Caution: This email originated from outside of the organization. DO NOT click 
links or open attachments unless you recognize or trust the sender.

Who can help me ID a flow switch with an adjustable range of triggering flow 
rates that can be used on a combined or PP system per 13D without ringing the 
bell upon operation of a plumbing fixture (or 2 or 3?)   Signal Safe has a 
switch with a range of 4-10 gpm but I don’t see where it’s adjustable for a 
specific flow rate in that range, only for the delay on the retard feature.  
Working with a homebuilder who is especially sensitive to fire safety and is 
pro-sprinkler, but like any developer they want to be as cost-efficient as 
possible.   We’re doing a deep-dive into PEX and CPVC and hybrids that use some 
of both, stand-alone, passive purge, fully integrated domestic/fire, and want 
to have options for jurisdictions that require an audible alarm.





 [cid:[email protected]]
Steve Leyton, President

T  |  619.255.8964 x 102  |  
www.protectiondesign.com<https://url.avanan.click/v2/r01/___https:/urldefense.com/v3/__http:/www.protectiondesign.com/__;!!OBed2aHXvKmHymw!xUP_44imxZbNarYK4A-T5bTTThDYa0yfWnYjTflMMWnrGIjCKgkSfp93-VfkONuBdgFUqckgAlRqJYwt2l_VlQhycZynMg$___.YXAzOnByb3RlY3Rpb25kZXNpZ25hbmRjb25zdWx0aW5nOmE6bzoyZGRjZTc0MjZlMzNjZjAwM2ViYjYwNDAzYzk5ZTY4NTo3Ojc3MTk6OGI3ZjI3ZGQwNWRjZjlkYzljNzU3OTViNGFmZGI3NDlkMmYyZWExYWEwMmU5NjQwMjg3ZTg4NTBmYzY5ZGNmYTpoOlQ6Rg>

2851 Camino Del Rio South  |  Suite 210 |  San Diego, CA  92108

Fire Protection System Design | Consulting | Planning | Training



_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://url.avanan.click/v2/r01/___https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org___.YXAzOnByb3RlY3Rpb25kZXNpZ25hbmRjb25zdWx0aW5nOmE6bzphZmM5MzM4OTAyYjJiNmZkNWFjMmI4MzNkOTVjMWNjZDo3OjE2NDM6Yzg0N2UwMmZiMjM1MGU4Yjc1NmU1YmNhZWU1NjE3YmMzNGJkMWIxMmRkYzIyNjM2ODg2ZDliNmMyY2Y5N2MxYTpoOlQ6Rg>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to