We have an existing building that does not require fire sprinklers but does 
have "limited area sprinkler protection" for the openings through smoke/fire 
walls for conveyors.  The system is old and utilizes the obsolete Tyco Thermal 
Control Valve at each opening to make it a mini deluge system for one open 
nozzle sprinkler at each opening.  I cannot find anything in NFPA 13(2019) or 
the IBC (2021) that would allow this now.  The owner wants to remove the TCV at 
each opening because they are starting to fail.  The areas are fully heated and 
it just doesn't make sense to me why they used a TCV to control one sprinkler 
with the bulb removed.  The TCV had a 200F solder link in it to activate it 
with the open nozzle sprinkler literally 6in away from the unit.   Could I just 
remove the TCV and install a sprinkler with a bulb at each opening?